G

gpz900jim

On ring mains, am i right in thinking that if you take the loop reading from the live, add it to the loop reading of the earth, divide it by 4, it should equal your r1 plus r2 reading (live and earth cross connected)? Cheers
 
it gives you an idea of what to expect. as ezzzy says, spurs will give you a higher reading on R1+R2 as the end/end res. of the ring does not see the spur/s.
 
as long as you know your r's from your elbow. but bear in mind, in an exam, just getting that wrong will lose you a lot of marks, and on a certificate would cause confusion, when the 17th amendment is supposed to do that.
 
Last edited:
Yes. Expressed mathematically:

R1+R2 = (r1+r2)/4

where;
r1 = end to end resistance of line on an RFC
r2 = end to end resistance of cpc on an RFC
R1 = resistance of line from MCB to furthest point on any circuit
R2 = resistance of cpc from earth bar to furthest point on any circuit
In the case of a perfect ring, R1+R2 is equal at all points (electrically there is no furthest point - all points are the same)
 
Some may think that getting terminology and symbols wrong doesn't really matter that much, but if you think you are ever going to do your 2391, then you should get used to getting it correct now, because failure to use the correct terminology is always a significant factor in it's high failure rate (see any Chief Examiners report - it's a common theme)

Correct terminology also enables us to discuss technical matters precisely and concisely without confusion. Where terminology is wrong confusion often ensues about what someone 'means'.
 

Reply to Ring main readings?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
793
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
979

Similar threads

In addition, can you show the junction box with the cover off? Isolate the supply first, obviously. It sounds strange, what you’ve described at...
Replies
2
Views
176
Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
946

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top