hello, a ring main should be one complete loop, to test a ring circuit which is two 3 core twin and earth cables ( generally ) you need to disconnect both cables, you will be left with 1 cable of 3 cores brown, blue, green and yellow and a second cable with brown, blue, green and yellow, carry out a continuity test between both brown cables ( call each end P1 for cable 1 brown and P2 for second cable brown ) between them P1 to P2 you should get a continuity reading ( for example say 0.5 ohms ) , carry out same step for neutral cables ( Blue ) calling them N1 to N2 and again you should get a reading of the same say 0.5 Ohms, do the same for the CPC and you should get a higher reading due the CpC being smaller that the neutral or phase conductor, connect P1 with N2 using connector block and P2 with N1 again using connector block. Carry out continuity test at each socket between phase and neutral, the reading from each circuit should be 1/4 of the total of P1 to P2 added with N1 to N2, if P1 to P2 + N1 to N2 = 0.5 + 0.5 = 1.0 ohms so each socket should read 0.25 ohms