Ring main testing | on ElectriciansForums

Discuss Ring main testing in the Australia area at ElectriciansForums.net

P

piz

hello I am confused rewired a house this week but I dont do much testing on the ring main as a domestic installer normal kitchen fitting radial cooker extra lights etc I rememberr being told this takes a bit of getting used to
this is what has happened so far r1 = 0.48 rn=0.72 r2=0.90 I know that we divide 2.5 by 1.5=1.666*by r1 this should be calculated cpc reading
then on my sheet it says R1+R2 I have cross connected live and cpc on the ring and gone around my sockets highest reading 0.41 is tis my R1+R2 or am I missing something and is R2 just measurment from cpc at cu to wurthest point on ring main ie half way please help
on top of this is the max disconnection time for tt 0.2sec found that in the regs

thought r1 and rn should be about the same might be clip not tight enough
please help
Thanks
 
Before you delve any further into calculating r1 + r2 / 4 you NEED to have your r1 & rn continuity readings equal (or very close)

I`d suggest you tighten that clip etc & start at the start again mate
 
ok check this one out kitchen sockets r1=0.12 rn=0.12 r2=0.21 better readings only 3 sockets on the ring but R1+R2=0.62 why??

Thanks lenny half scared dont like ring testing try to avoid but need to practise
 
Last edited by a moderator:
How do you test kitchen circuits when you have installed them?

Not being funny, but i am a little concerned that you are rewiring some ones house and have little understanding of the most important part of an installation.
 
I share the same concerns (altho it must be said, Piz is hardly alone is he?!?)

ok check this one out kitchen sockets r1=0.12 rn=0.12 r2=0.21 better readings only 3 sockets on the ring but R1+R2=0.62 why??

Thanks lenny half scared dont like ring testing try to avoid but need to practise

Jason`s valid point aside, if we`re to help you to improve your technical knowledge Piz, please ensure you`ve cross connected the T&E correctly - as in L1>E2 & L2>E1 :confused:

If you haven`t you`re simply not gonna get what you expect - readings will be all over the shop.

& you really shouldn`t be `scared` - you have isolated first haven`t you :eek:
 
Last edited by a moderator:
Hi Jason

reply tom your answer

r1 rn r2 end to end continuity

step 2
cross connect ph and net take readings should be r1+rn/4 approx

step3
cross connect
ph and cpc
check sockets should be approx r1+r2/4

then ins rest polarity ze pfc rcd etc


radial connect cpc and live at cu then test cpc and live at socket light etc

hope this makes sense
been a long day just cant understand if its the highest of step 2 or step3 we record
hope this makes sense let me know if you wouldnt do it like this
 
No need to stand aside.

I would rather people help than let someone cause themselves or someone else harm.

I was merely voicing my concerns and was not meant to offend or stop anyone giving advice.


Had a bad day:(


Edit:

piz

You record values of r1, rn & r2 end to end.

these tests are for RFC ONLY.

R1 + R2 is for all circuits.

Cross connecting r1 & r2 gives you your R1 & R2 values.

So its step 2 thats recorded
 
Last edited by a moderator:
sorry dont mean to upset anyone just wanted to prove I had a good idea how to do it think you find it looks ok I know spelling aint right and tests aint in order but thy would you be so concerned
 
sorry dont mean to upset anyone just wanted to prove I had a good idea how to do it think you find it looks ok I know spelling aint right and tests aint in order but thy would you be so concerned

You havent upset anyone (yet :D).

Testing of any circuit should be done and understood before they are energised.

Also, r1 & r2 are very different to R1 & R2, so spelling, in this instance does matter.:)
 

Reply to Ring main testing in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
853
  • Question
As long as you can carry out all the necessary testing, certification, are insured to do the work and all is carried out to Amendment 2 of the regs
Replies
1
Views
648

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top