hello I am confused rewired a house this week but I dont do much testing on the ring main as a domestic installer normal kitchen fitting radial cooker extra lights etc I rememberr being told this takes a bit of getting used to
this is what has happened so far r1 = 0.48 rn=0.72 r2=0.90 I know that we divide 2.5 by 1.5=1.666*by r1 this should be calculated cpc reading
then on my sheet it says R1+R2 I have cross connected live and cpc on the ring and gone around my sockets highest reading 0.41 is tis my R1+R2 or am I missing something and is R2 just measurment from cpc at cu to wurthest point on ring main ie half way please help
on top of this is the max disconnection time for tt 0.2sec found that in the regs

thought r1 and rn should be about the same might be clip not tight enough
please help
Thanks
 
hey piz
treat yourself it has all you need to know about testing and is worth a read
[ame=http://www.amazon.co.uk/exec/obidos/ASIN/0863418570/interactiveda3371-21]Guidance Note 3: Inspection and Testing Guidance Notes for Bs 7671: Jon Elliot: Amazon.co.uk: Books[/ame]
 

Reply to Ring main testing in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
853
  • Question
As long as you can carry out all the necessary testing, certification, are insured to do the work and all is carried out to Amendment 2 of the regs
Replies
1
Views
648

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top