hello I am confused rewired a house this week but I dont do much testing on the ring main as a domestic installer normal kitchen fitting radial cooker extra lights etc I rememberr being told this takes a bit of getting used to
this is what has happened so far r1 = 0.48 rn=0.72 r2=0.90 I know that we divide 2.5 by 1.5=1.666*by r1 this should be calculated cpc reading
then on my sheet it says R1+R2 I have cross connected live and cpc on the ring and gone around my sockets highest reading 0.41 is tis my R1+R2 or am I missing something and is R2 just measurment from cpc at cu to wurthest point on ring main ie half way please help
on top of this is the max disconnection time for tt 0.2sec found that in the regs

thought r1 and rn should be about the same might be clip not tight enough
please help
Thanks
 
hey piz
treat yourself it has all you need to know about testing and is worth a read
[ame=http://www.amazon.co.uk/exec/obidos/ASIN/0863418570/interactiveda3371-21]Guidance Note 3: Inspection and Testing Guidance Notes for Bs 7671: Jon Elliot: Amazon.co.uk: Books[/ame]
 
Got it aint read it for years
yellow book isbn 0-85296-991-0
must be ok ish passed the 2391 testing side of it but was about 5 yrs ago
is there a later edition ie 17th
 

Reply to the thread, titled "Ring main testing" which is posted in Australia on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top