J

JimmyB1988

Hi All,

Will post an introduction on the new members forum but need to blurt out my question while its still in my head.

Me and Mrs JimmyB1988 have moved into our first house, it has a split consumer unit, half on RCD half not, my sockets were on the half without an RCD. One breaker does all the sockets including the Kitchen. So I moved the sockets breaker over to the RCD side, moved the neutrals too over to the RCD neutral bar. But it keeps tripping the RCD, all works fine on non protected side, i insulation resistance tested the circuit and reads 0Mohms between line + neutral, neutral + earth, line + earth? Confused?
[ElectriciansForums.net] Ring Main Tripping RCD, Line to Earth reads 0


Can anyone think of anything obvious?

Thanks Guys/Girls
[ElectriciansForums.net] Ring Main Tripping RCD, Line to Earth reads 0
 
when u done a insulation resistance test did u remove the cables from the consumer unit ?
i see it hard to believe that u didn't have a problem before u moved it to the RCD side ? also like others have said have u removed all items from the sockets and isolated all spurs ? plus is there any neons on the circuit what could give u false readings ?
 
L/N/E all shorted together? Could be I suppose. Or is the OP mis-reading the tester and actually seeing an infinite resistance reading? Daz
 
Hi chaps , first post so hello to everyone.

One explanation could be a neutral to earth fault and the tester is picking up a reading through the connected load.

Not all switched spurs are double pole and can leave the neutral connected in which case if there was a neutral to earth fault then it will show up on L/E test as well.

Could be a problem with the boiler or maybe a some lighting taken off the ring through a spur somewhere.

Regards
 
Hi All,
Had another crack at it this evening

Tryed to be systematic, so identifyed one outgoing cable's conductors as L1, N1 and E1 using tape, other obviously is L2, N2 and E2
Checked the end to end resistance of each conductor on low ohms
L1 - L2 0.27 ohms
N1 - N2 0.27 ohms
E1 - E2 0.42 ohms

Then IR tested between L, N and E again.
L - N 0.00Mohms
N - E 0.00 Mohms
L - E 0.00 Mohms

As suggested then tested the same conductors using the low ohm setting.
L - N 28.8 ohms
L - E 30.1 ohms
N - E 0.14 ohms

Worrying figures, theres a short somewhere i think.

So next i split the ring, I disconnect the socket at the top of the landing, making two radials and from the DB i test each radial

L1 - N1 >99.99 Mohms
N1 - E1 >99.99 Mohms
L1 - E1 > 99.99 Mohms

L2 - N2 93.1 Kohms
N2 - E2 0.41 ohms
L2 - E2 93.2 k ohms

So my Cable 2 leg holds the fault, what do you guys think seems most likely from those readings?
 
Now you will have to narrow it down by dividing that leg , and testing as you do so , until you narrow it right down to one leg between 2 sockets , the fault could well be at one of the sockets ..
 
Had one of these on Monday, split the ring until I was able to identify 1 link between 2 sockets with an almost dead short L - E and on another link a IR reading of 0.35 N - E. Happy days. These things take time and I was doing this in a converted barn where the circuit was not laid out logically so it took a while to trace the links!
 

Reply to Ring Main Tripping RCD, Line to Earth reads 0 in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
310
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
932

Similar threads

  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
857
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
729

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top