Ring main with no earth ring!?! | on ElectriciansForums

Discuss Ring main with no earth ring!?! in the UK Electrical Forum area at ElectriciansForums.net

michaelw6

-
Arms
Joined
Apr 4, 2009
Messages
222
Reaction score
27
Location
swindon
Today i did a board change was one of them all in one eicr fix on site board changes "you know the ones that always go wrong".
Well the issue was the house ring.
i had 0.44 live 0.44 neutral and no earth ring.
I have put this circuit on a B32 61009 RCBO.
now how do i stand with the earth as its not to regs with regards sizing so theoretically if a fault develops it would not carry the load fast enough to trip.
I have had every point off in the house trying to find and tightened all up but no fault so it must be a joint under the floor. laminate down so floor coming up is a no go.
i thought about putting on a 20a but there are 20 sockets covering the whole house inc kitchen. so it may over load.
i thought about splitting ring but as i cannot find the fault how can i split ill have more sockets with no earth then...
So ive gone around and zs tested all sockets i have an earth max zs was 0.73ohms and the rcbo is max zs of 1.16ohms i believe so its well within tripping times.
Any more Ideas you recon it will be ok to leave just make a note of it on cert???
 
The ring must be split in between two sockets. My first job would be to find out between which 2 points it's split. (Disconnect all ring conductors at do. Link line and earth of one cable and test between these At the sockets, then once you've identified the sockets with continuity, repeat the process from the other end, I like to do a plan and record readings on it to try identify how the ring is wired) Then if possible rewire that section or split into two radials if this is feasible
 
Your max Zs is pretty irrelevant it is an rcbo, I know some may consider it poor practice to rely on the rcd to provide fault protection on TN systems, never the less a change from 32A to 20A is irrelevant.
 
Today i did a board change was one of them all in one eicr fix on site board changes "you know the ones that always go wrong".
Well the issue was the house ring.
i had 0.44 live 0.44 neutral and no earth ring.
I have put this circuit on a B32 61009 RCBO.
now how do i stand with the earth as its not to regs with regards sizing so theoretically if a fault develops it would not carry the load fast enough to trip.
I have had every point off in the house trying to find and tightened all up but no fault so it must be a joint under the floor. laminate down so floor coming up is a no go.
i thought about putting on a 20a but there are 20 sockets covering the whole house inc kitchen. so it may over load.
i thought about splitting ring but as i cannot find the fault how can i split ill have more sockets with no earth then...
So ive gone around and zs tested all sockets i have an earth max zs was 0.73ohms and the rcbo is max zs of 1.16ohms i believe so its well within tripping times.
Any more Ideas you recon it will be ok to leave just make a note of it on cert???
It's a Ring Final Circuit RFC NOT a blasted Ring Main:eek::oops::smilingimp:
 
Without r2 continuity, I can't see how you can obtain such a low Zs reading, obviously you have a parallel earth path via an appliance etc. If such an appliance is removed in the future the Zs figure will rise.

As the others said, time to locate the fault. Think Tel has suggested before to another OP, to split the RFC into two radials, if the break is somewhere you can't access.

Note to oneself, never do a CU change just before Xmas
 
Well I will make a note not to do any of those "All in one EICR fix on site board jobbies", they sound like hard work to me, specially as they are the ones that always go wrong. I had made a new years resolution not to be critical about anything anymore but je-sus-^^^ing-wept give me strength I just broke it early. Are you for real??? It says in your profile that your occupation is "electrical". What exactly is that???? Beam me up Scotty, take me now son.........
 
It's ok sparksburntout, it's only December 21st - the new you hasn't come into effect yet - LET RIP!
Well, this guy is, apparently, "the most trusted and best loved electrician in Swindon". Any other sparks in Swindon care to comment?? Are there any others?
Oh roll on 2017...
 
Well I will make a note not to do any of those "All in one EICR fix on site board jobbies", they sound like hard work to me, specially as they are the ones that always go wrong. I had made a new years resolution not to be critical about anything anymore but je-sus-^^^ing-wept give me strength I just broke it early. Are you for real??? It says in your profile that your occupation is "electrical". What exactly is that???? Beam me up Scotty, take me now son.........

I go through this love/hate relationship with your posts, gonna start calling you marmite!:)
 

Reply to Ring main with no earth ring!?! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
299
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
282
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
355

Similar threads

  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
831
You would treat it as a TT installation.
2
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • exceeding voltage drop
    The cable is way undersized. If the voltage drop is detrimental to the installation I would make...
  • TT advise
    OK My take on the precautions to implement when omitting an up front RCD on a TT system. Tails...
  • SIL vs ATEX
    Good morning all, I have a question for those who are CompEx and SIL aware - I have various Ex...
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top