I’m rewiring a bungalow and the owner has asked for a radial for all sockets except the kitchen. But there will be a separate washer and dryer in the circuit. Will a 20A radial be enough?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Ring or radial in bungalow in the UK Electrical Forum area at ElectriciansForums.net
I don't quit grasp this bit, how often do you chase in a groove that is just wide enough and deep enough for a single T&E run?Sorry a bit of additional info. The reason for the radial sockets is that he’s doing all the chasing (great) but wants to minimise it because he’s living there during the rewire
And quite probably two runs back to the CU should it need more than 20AAre you not getting the irony of this. A radial will require two cables, the same as a ring final apart from the last outlet.
There is the option of having hidden JB for each socket, with each one as a branch off the radial, but really the maintenance implications of dozens of JB would horrify me unless all in attic so accessible (not floored, etc, so they are hidden).
In what way do you anticipate that minimising it? It eliminates 1 single cable run and severely limits the capacity of the circuit, doubt 4mm will be up to a 32a radial if serving the entire house unless it’s specifically installed to a certain installation method.Sorry a bit of additional info. The reason for the radial sockets is that he’s doing all the chasing (great) but wants to minimise it because he’s living there during the rewire
so put the washer and dryer on a 4mm 32A radial.Yes. The kitchen to be on a ring, and the rest of the house on a radial (except boiler etc)
so put the washer and dryer on a 4mm 32A radial.
but that's 2 cables instead of 1, 2 MCB/RCBOs.. twice the effort and twice more expense.Or pull 2x 2.5 16/20A radials for these appliances.
but that's 2 cables instead of 1, 2 MCB/RCBOs.. twice the effort and twice more expense.