Hi all,

DIYer here. My garage has a double socket fed by 4mm2 twin and earth connected to the same circuit breaker has the ring main for the sockets upstairs in the house. The MCB is a B32.

Is the feed in the garage considered a spur from the ring main or is it a separate radial circuit which happens to be on the same MCB? Ideally I'd like to add more sockets to the circuit in the garage (using 4mm2) but is this safe or allowed?

Thanks.
 
The more I read this thread the more confusing it becomes.

As far as I see it,

There is nothing wrong with a spur on a Rfc taken from the CU.
Its in the OSG 7.2.2 para 4.

The spur would normally be in 2.5mm2, but the fact that it's in 4mm2 is not a problem. (Might be a big garage, VD and all that)

If the socket is replaced with a FCU then there's no limit on how many sockets can be connected to the load side, as long as your happy with the 13 amp limitation.

As this is not a new circuit then it does not require Part P notification.
 
Is this because it's on a B32 MCB?
It's a spur from a 2.5mm2 RFC albeit from the CU, no problem with that, why 4.0mm2 was used is a mystery, it makes no difference to what you can and can't add, a spur is a spur, one twin or single socket only fed directly from the RFC without a FCU involved. Nothing to do with the B32 Amp CB rules is rules is rules.
 
Last edited:
As pete said, there isn't a rule, but there's nothing preventing it. Cable sizing in the guides are the "minimum " requirements.

We don't know the cable size in the RFC that the spur is connected to. The op has never declared that. The whole thing could be in 4mm2. It's pure speculation on our part that's its 2.5mm2 because that's the norm.
 
As pete said, there isn't a rule, but there's nothing preventing it. Cable sizing in the guides are the "minimum " requirements.

We don't know the cable size in the RFC that the spur is connected to. The op has never declared that. The whole thing could be in 4mm2. It's pure speculation on our part that's its 2.5mm2 because that's the norm.
And the fact that the OP has mentioned 4.0mm2 on several occasions, but yes the assumption is/was that it is a RFC wired in 2.5mm2 cable. Thanks for pointing that out.:D
 

Reply to Ring spurred at origin? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
316
  • Question
Thanks for the advice.
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top