ring testing | on ElectriciansForums

Discuss ring testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

F

foghorn

whilst doing ring continuity i have no end to end on cpc also on isulation test live earth im getting 9.50Meg ohmson the same ring are these two results to do with the same problem if so how can i go about finding the fault am i right in saying that if i spilt the ring at one of the sockets then check continuity on each earth at all other sockets i should find the break in cpc wilol this give me low insulation readind live earth.
 
scratching my head with this cant locate broken earth had all sockets of replaced several still no cpc end to end im thinking that the low insulation test has something to do with no cpc end to end
 
Wonder if someone has nailed a picture hook into the wall and its gone through the CPC and clipped the line insulation, then at a later date the hook has been removed.
 
Disconnect the earths and carry out earth continuity test using the wander lead, this should help locate where the break is.
As amp David says 9.3mohms is a pass even if not as high as the other tests
 
Last edited:
so does that mean disconnect both earths at the sockets and go round doing the same at all sockets belling out each aerth at every socket
 
landing light wired weird 2way common upstairs go straight to landing light L1 and L2 links to down stairs 2 way common taken from common of 2 gang switch
 
so does that mean disconnect both earths at the sockets and go round doing the same at all sockets belling out each aerth at every socket

No, test from one earth leg at the consumer unit to each socket outlet, if there is a break the the reading will increase the nearer you get to the break.
 

Reply to ring testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
280
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top