Had a call out to a home where the RCD keeps tripping when lounge ,dinning and bed room sockets mcb is switched on. Fault traced to one of the legs from the consumer unit to 1st socket 0.2Meg ohm at best. cable size is 2.5mm T&E there are 10 double and 4 single sockets on the circuit. Reg 433.1 seems to indicate that providing the floor area is limited to 50 m2 (the area in question is 3/4 the floor area of a medium size house. it would be ok to drop out the damaged leg from the consumer unit and socket fuse down to 20Amp mcb and leave as is. Possible to rewire initial leg and reinstate ring but do I need too?

what do you think?

AdieB

PS dropped leg out of consumer unit marked cable with tape and description of fault. Disconnected from socket and put wago type terminals on he cores. Changed mcb to16A (close's that was on van.)
 
just explain to the customer that he's limited as too the load on the radial. give him a price to replace the damaged cable, then let him decide, once he has the facts.
 
Only things plugged in would be TV, Sky, answer machine ,and maybe clock radio. Customer needs work done straight away as visitors arriving . Due to other commitments can't get there until next week.
adieB
 
Only things plugged in would be TV, Sky, answer machine ,and maybe clock radio. Customer needs work done straight away as visitors arriving . Due to other commitments can't get there until next week.
adieB

replace the duff leg, keep it as a RFC, 3 hours job done, simples
 
I have always been a Ring circuit kind of Guy (Old school). I thought that the new school is for radial circuits, as most hosing now has central heating and the power consumption on the power side is less than 20 Amp.

AdieB
 
Possible to rewire initial leg and reinstate ring but do I need too?

what do you think?


What do I think?

Stop being idle and get on with replacing the faulty leg and reinstate the ring.

Had the fault been at a mid point I may have agreed with making it two radials. No way would I agree to making a single radial and down rating by 62%.
 
What do I think?

Stop being idle and get on with replacing the faulty leg and reinstate the ring.

Had the fault been at a mid point I may have agreed with making it two radials. No way would I agree to making a single radial and down rating by 62%.

A little unfair. There could be many reasons why the client does not want it re-wired. Decorations etc. if the loading is taken into account then surely everyone is a winner.
 

Reply to Ring to radial in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
650
  • Question
Why aren't you asking them?
Replies
5
Views
829

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top