AdieB

-
Joined
Apr 1, 2012
Messages
76
Reaction score
6
Location
Dorset
Had a call out to a home where the RCD keeps tripping when lounge ,dinning and bed room sockets mcb is switched on. Fault traced to one of the legs from the consumer unit to 1st socket 0.2Meg ohm at best. cable size is 2.5mm T&E there are 10 double and 4 single sockets on the circuit. Reg 433.1 seems to indicate that providing the floor area is limited to 50 m2 (the area in question is 3/4 the floor area of a medium size house. it would be ok to drop out the damaged leg from the consumer unit and socket fuse down to 20Amp mcb and leave as is. Possible to rewire initial leg and reinstate ring but do I need too?

what do you think?

AdieB

PS dropped leg out of consumer unit marked cable with tape and description of fault. Disconnected from socket and put wago type terminals on he cores. Changed mcb to16A (close's that was on van.)
 
Uk It wasn't long ago that you were complaining that members were having a pop at you all the time!!
It cuts both ways. A debate is one thing, baiting another member is another thing.

Point taken. Apologies. My point that in all reality this is not worth a design still stands. I just think he does this for the sake of argument.
 
Pure laziness. Besides what happens if the RCD fails?

Replace the faulty leg get it back to how it was before and get paid.
Hang on, that's the customers decision, not yours, I'd have no problem doing either. Give the client the options if they want limited capacity or reinstate the RFC. Also Dilb, I would test RCD in the course of my work. If you think down that track, what if the MCB fails? what if a mouse eats the cable insulation? what if there is a power surge? What if, What if, What if?
 
I really think any spark worth their salt would give the client two options:

1) reinstate ring (surface or chased)
2) change to a radial circuit

cable calcs are done. In the head of a guy who has enough experience to make these calls.
 
Had a call out to a home where the RCD keeps tripping when lounge ,dinning and bed room sockets mcb is switched on. Fault traced to one of the legs from the consumer unit to 1st socket 0.2Meg ohm at best. cable size is 2.5mm T&E there are 10 double and 4 single sockets on the circuit. Reg 433.1 seems to indicate that providing the floor area is limited to 50 m2 (the area in question is 3/4 the floor area of a medium size house. it would be ok to drop out the damaged leg from the consumer unit and socket fuse down to 20Amp mcb and leave as is. Possible to rewire initial leg and reinstate ring but do I need too?

what do you think?

AdieB

PS dropped leg out of consumer unit marked cable with tape and description of fault. Disconnected from socket and put wago type terminals on he cores. Changed mcb to16A (close's that was on van.)


0.2MΩ isn't anywhere near enough to trip an RCD, it needs to be closer to 0.008MΩ so perhaps some more investigation is required. Could you confirm what the poor IR test results refer to? L-N or N-E? I have to assume N-E, but it would be good to just know for sure as 0.2MΩ does sound like something plugged in or a neon?

It's not impossible for there to be a fault with the actual cable run but it's much more likely that the fault lies with an appliance or at a socket/FCU. Have you made absolutely certain that there are no other connections between the CU and this '1st' socket. Perhaps hidden in a cupboard?

As for changing to a radial, I think that is an option once some more investigation has taken place to find the fault. Also, like the others have said the floor space would have to be <50²m and the Electricians Guide to the Building Regs suggests <40m total run length as well. Also I would want to work out what the max demand is 'likely' to be for this circuit before changing to a 20A radial, this could affect your decision.

But.. it also depends on how 'Possible to rewire initial leg' it is if you do find the fault to be hidden in the fabric of the building? If it's easy then decision made, if not then you may sway towards a radial.
 
0.2MΩ isn't anywhere near enough to trip an RCD, it needs to be closer to 0.008MΩ so perhaps some more investigation is required. Could you confirm what the poor IR test results refer to? L-N or N-E? I have to assume N-E, but it would be good to just know for sure as 0.2MΩ does sound like something plugged in or a neon?
.
There will be other earth leakage in parallel with this 0.02M/Ohm circuit N-E issue. Also a L-N fault would not trip RCD, it must be L-E or N-E for earth leakage. I would hope he has disconnected all loads.
 
There will be other earth leakage in parallel with this 0.02M/Ohm circuit N-E issue. Also a L-N fault would not trip RCD, it must be L-E or N-E for earth leakage. I would hope he has disconnected all loads.

I realise this TJ, but it would just be nice to see it written clearly, much easier to form an opinion then. Also it was 200,000Ω not 20,000Ω, 200,000 is a long way from 8,000 so thats a lot of parallel earth leakage!
 
Last edited:
Even if Zs was a bit over for MCB, which it almost certainly won't be, I would have no problem in utilising the 30ma RCD to provide satisfactory earth fault disconnection in this instance. This is not designing new circuits, this is getting someone up and running when they have a problem.

As a temporary measure then yes. NOT as a permanent fix!

As for relying on the RCD, is this the depth the trade has sunk where supplementary protection has changed its role?
 

Reply to Ring to radial in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
650
  • Question
Why aren't you asking them?
Replies
5
Views
829

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top