Ring keeps tripping ... end to end .65/.65/1.2 IR 999 on both legs 999 together ....but trips rcd straight away any ideas
 
Does it trip the RCD when you power up the circuit or is it just intermittently?

When you're carrying out the IR test, does your MFT simply run the test and stop or is it like a Megger where you hold the button down and it keeps applying the test voltage and providing readings? I would run a longer test and look for sudden drops in the IR reading. If you get them it can sometimes indicate you have a pinhole in the insulation that won't always show up on a quick test. In which case, investigate any of the accessories you might have worked on or the whole lot if this is a new fault.
 
The Opening post isn't clear.
How are you carrying out IR tests ?

It is possible for a circuit to pass an insulation resistance test when testing between its own conductors, if its isolated from everything else. ( E and N removed from DB)

Something like a screw just piecing through the insulation and touching the live conductor whilst also touching a copper pipe would show the same results.

You need to be more specific.
 
The Opening post isn't clear.
How are you carrying out IR tests ?

It is possible for a circuit to pass an insulation resistance test when testing between its own conductors, if its isolated from everything else. ( E and N removed from DB)

Something like a screw just piecing through the insulation and touching the live conductor whilst also touching a copper pipe would show the same results.

You need to be more specific.

A very good point made.

When conducting IR tests, the cpc should ALWAYS be connected to the earth bar in the CU along with ALL the other CPCs
 

Reply to Ring tripping rcd when connected in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
338
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
759

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top