Which is it for you.......


  • Total voters
    72
It's a hypothetical question..
32a Mcb is overrated for a 2.5 radial, but chuck a couple of cables in and suddenly it's okay..

A 32A MCB is overrated for a radial circuit run in 2.5 but it is not incorrect for one double (or single) socket outlet on 2.5.
Because the nature of the load is such that you cannot have an overload as the socket outlets will use fused plugs that limit the maximum current.

So where there is a situation where there cannot be an overload there is no requirement to provide overload protection, only fault protection and the MCB will provide fault protection.

In your example having a single spur off the MCB for a ring and then removing the ring would be still compliant with the regulations, however you would not be able to add outlets to this (now) radial.
 
A 32A MCB is overrated for a radial circuit run in 2.5 but it is not incorrect for one double (or single) socket outlet on 2.5.
Because the nature of the load is such that you cannot have an overload as the socket outlets will use fused plugs that limit the maximum current.

So where there is a situation where there cannot be an overload there is no requirement to provide overload protection, only fault protection and the MCB will provide fault protection.

In your example having a single spur off the MCB for a ring and then removing the ring would be still compliant with the regulations, however you would not be able to add outlets to this (now) radial.

Okay I see your point now.

Thanks.
 
are you not doubling your csa with a ring making the load you can draw off it higher hence 32a mcb does this not make the ring better for handling more load being drawn off any socket on it ?
 
hi there

Reading this thread with interest, changing the subject slightly how are grid switches wired for kitchens, these are becoming more common
Many Thanks
 
hi there

Reading this thread with interest, changing the subject slightly how are grid switches wired for kitchens, these are becoming more common
Many Thanks

Boy i think your right on the "Changing the subject slightly" certainly not on a ring main..
 
hi there

Reading this thread with interest, changing the subject slightly how are grid switches wired for kitchens, these are becoming more common
Many Thanks

ring or 32a radial to grid box then 2.5 t&e branches to each appliance.
would be one way. :-)
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

kingeri

Arms
-
Joined
Location
Yorkshire

Thread Information

Title
Ring vs Radial
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
189

Advert

Thread statistics

Created
kingeri,
Last reply from
Dan,
Replies
189
Views
27,857

Advert

TrueNAS JBOD Storage Server

Back
Top