I keep hearing the reason why ringmains are dangeous is because if there is a loose connection or a break you'll pull twice the current at the break

I have never heard of this and think there totally talking out there buttholes

Can you confirm that they are
 
On a ring main you have two conductors in parallel each carrying (approximately) half the current that is drawn by the circuit. If you break the ring then all the current will be carried by only one conductor. This can be considered as drawing twice the current but it is better to say that the total current is now carried by one conductor. This could well overload the current carrying capacity of that conductor since it is not designed for that loading.
 
It's not so much that conductors will have to carry the full current, which might not actually be any more than they would carry in normall use.
It's more to do with the fact, that the break would not be noticed, whereas with a radial it would
 
2.5mm cable is only rated at around 20amps so if the ring final is broken then in effect the ring has become two radial circuits in which the circuit protective device is rated at 32AMPS and as the cable is only rated around 20AMPS there is a possibility that the cable could potentially become over loaded and become damaged before the MCB would trip.
This is why it is dangerous if the ring is broken.
 

Reply to ringmain in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
166
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

thank you so much. that worked out. i ended up shorting the live switch and sparks flew, but i recovered and its all working now. :)
Replies
3
Views
273
  • Sticky
So, how do we perform a DGA? Let's assume there's no analyser attached to the TX. We need to get a sample of oil out of the transformer. Different...
    • Informative
    • Winner
    • Like
Replies
2
Views
650

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top