What is DGA? Dissolved Gas Analysis.
This is just a VERY basic explanation of DGA.
Power transformers use oil as both an insulator and for cooling. Under normal conditions the oil will contain assorted gasses such as C0, C02 and Hydrogen. As the oil ages or under fault conditions the oil can, over time, break down releaseing gasses. By measuring the gasses and the speed in which they are increasing we can work out what, if any, fault is going on in the transformer. A healthy transformer will have relatively steady gas levels. If one or more gasses start to rise then we can determine what's going on inside the tank and deal with it. Different faults produce different gasses. For example, a while ago I took an oil sample from a TX, analysed it and found higher than previous levels of acetylene. This is a big red flag. Resampled a week later and risen once again. Acetylene is produced during arcing in oil so we knew it was serious. The power station took the transformer out of service. We drained off enough oil to look inside and found a connection was black. It had worked loose and was arcing. So DGA can save the life of a transformer.
How is DGA performed? Either by manual sampling and analysis or by online DGA where an analyser is bolted to the transformer and the oil continuously monitored. More about that tomorrow.
 
So, how do we perform a DGA? Let's assume there's no analyser attached to the TX. We need to get a sample of oil out of the transformer. Different labs will have different requests but you'll either need a 100ml syringe or a 500ml bottle.Clean the valve, run off 500ml of oil, scrap that then run off another 500ml or syringe of oil. Simple. Okay, what now? Well, take it to the lab or run it through an analyser. We do a mixture depending on what the site wants. We have our own portable analyser so I can take the sample and give the client the results within minutes. Bl00dy expensive bit of kit though.
20240616_104033.jpgThe unit on the right is a titrator. It measures the moisture content in the oil. The max permitted is 35ppm of moisture
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Moley

Esteemed
Arms
Supporter
-
Joined
Location
Pontypridd, S.Wales
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other
If other, please explain
High voltage & EHV field service engineer

Thread Information

Title
W2D4 - DGA What is it and why do we do it?
Prefix
N/A
Forum
Electrical Engineering Chat
Start date
Last reply date
Replies
2

Thread Tags

Tags Tags
None

Advert

Thread statistics

Created
Moley,
Last reply from
Moley,
Replies
2
Views
699

Advert

Back
Top