Hi Guys,
does anyone know of any specific codes of practice, standards or wiring diagrams I can reference for wiring power and manual control switches to multiple roller shutters covering office windows. Im attempting to resolve a contractual dispute and need evidence based information.
regards
Joesdad
Hi Guys,
regards
Joesdad
Try the shutter manufacturer
Hi Guys,
regards
Joesdad
One question, are these security shutters that are closed when a business is closed or are these entrance/exit shutters as you get on loading bays etc?
Perhaps if you actually explain, as best able, what the problem is and why it is a problem then perhaps we will all have a better idea of how to assist or guide you in the right direction.
The shutters are manually operated from within the office in groups and secure ground floor office windows out of office hours. The building has been rewired retaining the legacy shutters. I have a contra charge for repairs to motors and limit switches as the motors drove the blinds through the (failed) limit switches when operated
OK, did you do the rewire work? Why did the limit switches fail, had they been rewired to contactors to shut of the motor supply as before or were these missed out, was this work part of the spec for the rewire, if not your not liable...Information please.
I wouldn't have thought a building rewire would extend to rewiring the shutter control wiring.
Are we talking about 3 phase power to shutters,, went up when should have gone down?
Hence my question, if the control wiring has been partially or totally ripped out or otherwise bypassed it would explain if the shutters have power why the safety circuit would not operate, the key is to whether the control circuit was in the rewire spec or if they only had to provide power to point A etc. If the latter then I do not see how they could be responsible unless it could be demonstrated that some action they took has caused the problem
The classic case of reversed phase rotation.
Anything that moves to a final limit should be at the centre position before anything is done to the supply. If it goes the wrong way, it won’t do any damage! The limits WON’T work when the drive is reversed.
Reversed the up limit will stop it going down the down limit will stop it going up. It’s basic engineering!
Get the cheque book out, it’s you’re fault.
even with reverse rotation i would expect limiter switches to be installed on both up and down modes, so cant see a damage done here, but would suggest getting phases correct in the first place
Yes but the N/C limit switch will be on the wrong relay/contactor coil.
So if the motor is running the wrong way (phase rotation wrong), then the wrong limit switch will be operating on the de-energised coil and will not stop the shutter.