It's a bit of a push to say we all install bolts and banjos, I for one haven't installed banjos on SWA for a good year now at least.
 
The reason I ask this is because I was picked up on it a few years ago by another sparks, the board I had installed was an MEM and after phoning them they confirmed that the complete enclosure was tested as an adequate part of the earth and no connection to the earth bar would be required and would not improve the situation
 
Ok, if you install a banjo with a bolt then you put an earth lead to the earth terminal.
If you are going to use the metal enclosure as the earth then you don't need a banjo in the first place, you just clean it back to shiny metal where the gland will sit.
 
Yep, I totally agree with that, the only thing I can think that might improve the situation is if you put the banjo on then a lock nut before putting it through the enclosure, otherwise on a metal dis board it does not improve the reliability of the earth
 
Taking the gland plate off and replacing it with a brass one gets my vote for lots of SWAs into one DB.
 
Yep, I totally agree with that, the only thing I can think that might improve the situation is if you put the banjo on then a lock nut before putting it through the enclosure, otherwise on a metal dis board it does not improve the reliability of the earth

How would the locknut help?

A paint cutting/jagged/serrated washer might help.

I prefer to use piranha nuts these days unless I have a lot of SWA terminating in the same place.
 
I'm just considering if it comes loose, if its tight then it should have a good connection, if its loose it won't have a good connection whether it has a banjo or not but if it had a banjo with another locknut separate to the enclosure that could help, but the spring type washer is a good idea
 
All academic really unless you state whether the armour is the cpc as in a 2 core or a 4 core tp&n.
A 3 core used as an sp&n supply will have a core available for cpc use and the armour is then containment only.
Completely different scenarios.

Boydy.
 
In what way is it different, the armour must be connected to earth in an electrically and mechanically sound manner in both situations.
 
if you are going to go to the trouble of getting nylocks to go with them, why not just get proper bolts in the first place?
 
I think the main point is, is it part of the wiring system? Tray could be considered part of the wiring system, think about earthing cabinets containing electrical equipment, this would be to ensure the cabinet does not become live in the case of a fault, similarly for tray, though I would say the likelihood is low if the cables were all SWA.
 
Thanks Richard.

I understand what u are saying about cabinets ect, but tray using swa I see different it could only as I see inadvertently become and earthed part due to insulation coming off the swa.
I primarily work in commercial industrial environments. I have only ever see tray earthed twice. Usually I thought belts and braces attitude. Gn8 also states something along the lines of this too.
Although I read the beama guide with interest.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Roofing Bolts as Earthing studs
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
68

Thread Tags

Advert

Thread statistics

Created
jim1976,
Last reply from
jamie-spark,
Replies
68
Views
11,394

Advert

Back
Top