Roofing Bolts as Earthing studs | Page 3 | on ElectriciansForums

Discuss Roofing Bolts as Earthing studs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Cable tray isn't required to have any earth continuity, or even be bonded.
Whereas the connection to the banjo is a connection of the CPC.

Sorry mate, have to disagree!!

From the BEAMA (BS EN 61537) guide:

"2.10.2 Electrical continuity
Cable ladder and cable tray systems that are electrically conductive should have
adequate electrical continuity to ensure equipotential bonding and connections to earth.
Installations shall comply with the requirements of BS 7671 (The Wiring Regulations)."
 
I bond every tray installation that I do!

Likewise. Tray/Ladder/Basket..... I think the only thing I'd say doesn't need it is cable hooks for temporary looms (found mostly in entertainment and TV world for getting looms inside>out to OB trucks and the like).
 
To make a reliable connection you need the contact surfaces to be clean, flat, mechanically secure and gas-tight, which means the fasteners ought to be well made, with flat surfaces and effective threads that provide a definite minimum clamping force for a given tightening torque. Roofing bolts are not made to the same spec as hex set screws and I don't trust them to achieve this. The compromise design of the head makes it difficult to torque up accurately and the large diameter makes it easier for movement of the lug to rotate it and loosen the connection.

N/P brass hex for me every time for banjos and cable lugs, BZP steel bolts on tray & trunking where all surfaces are galv anyway.
 
Sorry mate, have to disagree!!

From the BEAMA (BS EN 61537) guide:

"2.10.2 Electrical continuity
Cable ladder and cable tray systems that are electrically conductive should have
adequate electrical continuity to ensure equipotential bonding and connections to earth.
Installations shall comply with the requirements of BS 7671 (The Wiring Regulations)."

Interesting, I used to insist on all tray and basket being bonded until i was advised otherwise on a forum.

I'll offer up guidance note 8 item 10.11 on page 157 as evidence for my post above.
 
the reason for that is because tray is not an enclosure whereas trunking is. the tray is still an exposed conductive part of the installation.

I know the reason is because it does not contain the cables - hence is a cable support rather than containment. However, as it cannot have unsheathed cables it is not an exposed conductive part. Usually jobs require cable tray to be earthed so generally it is done, however it wouldn't be correct to state that there is a requirement to do so.

And indeed there could be arguments as to why it shouldn't be.
 
The reason I ask this is because I was picked up on it a few years ago by another sparks, the board I had installed was an MEM and after phoning them they confirmed that the complete enclosure was tested as an adequate part of the earth and no connection to the earth bar would be required and would not improve the situation
 
Ok, if you install a banjo with a bolt then you put an earth lead to the earth terminal.
If you are going to use the metal enclosure as the earth then you don't need a banjo in the first place, you just clean it back to shiny metal where the gland will sit.
 
Yep, I totally agree with that, the only thing I can think that might improve the situation is if you put the banjo on then a lock nut before putting it through the enclosure, otherwise on a metal dis board it does not improve the reliability of the earth
 

Reply to Roofing Bolts as Earthing studs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
527
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
915

Similar threads

  • Question
"A catalogue of errors" would be the appropriate phrase here and I agree with Avo and James that HSE need to be involved rather than this forum...
Replies
4
Views
2K
  • Question
Nothing wrong with it. Which manufacturers have you got this information from? What do you mean by trip speed? Fuses and MCBs can operate in the...
Replies
11
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top