Already been stated....#10 and #11
True, things just seemed to be going off at bit of a tangent
![Smile :) :)](https://cdn.jsdelivr.net/gh/twitter/twemoji@14.0.2/assets/72x72/1f642.png)
OP's question was quite simple to answer. The TRVs only control the heat of the rads but not the boiler. The room stat is there to turn the boiler off and on. Without it you'd have to manually turn it on and off or it'd be on all the time (until overheat).
Doesn't the boiler have its own 'stat on the return water? Placing a thermostat in an unheated room will not control the boiler since it will be on all the time. And since I only turn the rads on (with the TVR) in the room I am occupying I would need to carry the 'stat around with me for it to be effective![]()
The stat should not be fitted in an unheated room
The heating system shall be provided with means to limit the temperature of the spaces it is heating.
Where individual thermostatic radiator valves (TRVs) are used they shall not be the sole means of control for the heating circuit but shall be used in conjunction with other controls which ensure that the boiler is shut off, or reduced to minimum burning rate for solid fuel, when not required.
Absolutely, otherwise it would be a waste of time.
The BS says:The BS says:
Fair enough if that is the regs. But which room should |I put the 'stat in bearing in mind that any room in the house can be unheated at some time or other.