Routing of earth cables... | Page 2 | on ElectriciansForums
Discuss Routing of earth cables... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I think its more about the rating of the cable . Not what voltage its carrying. Eg you could run a fp200 fire alarm cable with mains voltage cables because fp is rated up to 600v even though its only carrying 24v
No you can't. Fire cables have to be separated from LV and ELV cables. Correct me if I'm wrong though (this is just what we were told at College).
you are correct. 528.1, note 2,(refer to BS5266 and BS5839). and 560.7.1 and 560.7.7.
Reply to Routing of earth cables... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I see no issue with this, it sounds like a relatively normal installation. The use of insulated and sheathed cables inside steel trunking is a...
davesparks
Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
loz2754
L