Due to an increase in load for a subman, I now need 2 phases for an outbuilding. Original design was 63a supply, but now an electric shower and another ac unit has been added due to a design error.
Questions are, can you get a 2phase mcb to fit a schnider PoN board? Are you allowed to supply 2 phases in one cable switched by single pole mcb via an isolator with labels warning of two sources of supply? Can I use a 3 phase mcb with L3 spare? (99% sure I cant)
Submain is a 3 core, fed via isolator via 3 phase 24 way db, with L3 spare.Unless I can find a safe method to use what was the earth core as a phase, the load will trip its MCB.
The house is supplied with a 2 phase supply I managed to get architects to agree to let me utilise due to the demand for the house. Client does not seem to think its important to consult them with changes, but even if he did they don't seem to have a clue what they are doing. My manager doesn't seem to give a dam as he's leaving, and it's me that's going to be left in the lurch with no-one with the expertise or know how in the office.
Any advice except walking of site welcome!
Questions are, can you get a 2phase mcb to fit a schnider PoN board? Are you allowed to supply 2 phases in one cable switched by single pole mcb via an isolator with labels warning of two sources of supply? Can I use a 3 phase mcb with L3 spare? (99% sure I cant)
Submain is a 3 core, fed via isolator via 3 phase 24 way db, with L3 spare.Unless I can find a safe method to use what was the earth core as a phase, the load will trip its MCB.
The house is supplied with a 2 phase supply I managed to get architects to agree to let me utilise due to the demand for the house. Client does not seem to think its important to consult them with changes, but even if he did they don't seem to have a clue what they are doing. My manager doesn't seem to give a dam as he's leaving, and it's me that's going to be left in the lurch with no-one with the expertise or know how in the office.
Any advice except walking of site welcome!