Hi guys

I was putting in a spur socket at a friend's house. when i noticed that the CPC is the metal cable trunking. I understand this is within regulations. However upon testing it had a high earth loop impedance and likewise r2.

My question is, is it acceptable to run in a new CPC from consumer unit MET to the relevant outlets, but using a different cable route (plastic trunking etc)

Thanks Marcus
 
Have you tried tightening the conduit termination at the board.

Yes indeed, and checked earth bond
[automerge]1583434172[/automerge]
So after a lot of swearing I managed to get a new CPC down the conduit, draw tape was not much use and there was loads of brick, concrete and plaster that had fallen down conduit over the years. As the immersion heater is soon to be no longer needed due to combi boiler going in I used the neutral conductor for it to pull though the CPC, all good now

Also found out the light switches are earthed via conduit, just the one I picked to look at the conduit was not attached to the back box haha

Thanks for you guys help and suggestions
 

Reply to Running in a new CPC in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
486
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
956
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
900

Similar threads

  • Question
It's the same with any system, if you put poo in, you get poo out!
Replies
4
Views
2K
Good question now to start with thermosetting insulated conductors are not tri-rated that is something different. Table 4E1A deals with this type...
Replies
1
Views
270

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top