Hi, I'm looking for some advice regarding running of distribution cable around a warehouse. My client is having a new 200A supply installed but this will be on a different wall approx 20m away from the existing 100A supply. I need to run a cable from the new supply to the existing busbar chamber and I'm looking for advice on which cable and containment methods would be best. There are a cables, conduits and pipes I would need to get over on the way. Any help would be greatly appreciated.
 
That's true, although there is racking along the block work and there's a good chance of the cable being crushed by forklifts loading and unloading the racking
Wouldn't be much of a fork lift driver if he hit the racking and the cable, have to be going some to crush a 70mm2 SWA
 
Ok. Thanks for all your advice. It's very much appreciated. I've just been reading through the WPD paperwork and it specifies that "The tails should be Tri-rated cable" Does anyone know if SWA is classed as Tri-rated?
 
Ok. Thanks for all your advice. It's very much appreciated. I've just been reading through the WPD paperwork and it specifies that "The tails should be Tri-rated cable" Does anyone know if SWA is classed as Tri-rated?
Trunking it will be then, does that answer your question? Mark you need to take stock, do you think in all honesty you are up to doing this work.
 
Trunking it will be then, does that answer your question? Mark you need to take stock, do you think in all honesty you are up to doing this work.
It confirms what I already had in mind to an extent. I thought I would ask others their advice incase there was a better way. Why would I not be up to doing this work Pete?
 
It confirms what I already had in mind to an extent. I thought I would ask others their advice incase there was a better way. Why would I not be up to doing this work Pete?
Some of the questions you have asked, I really didn't intend to be rude or disrespectful Mark
 
Obviously you have a better idea of any possible issues with any of our suggestions because you know the layout first hand

From what I can see,you have a lot of blockwork to play with on the door wall, perhaps you could make use of that lower wall by sitting it on the top of the blocks (not sure if you need to pass that steel upright)
 
Obviously you have a better idea of any possible issues with any of our suggestions because you know the layout first hand

From what I can see,you have a lot of blockwork to play with on the door wall, perhaps you could make use of that lower wall by sitting it on the top of the blocks (not sure if you need to pass that steel upright)
There are obstacles galore Des. It's not a straight run by any stretch of the imagination. I haven't got the most experience with tray and trunking so was hoping for some inspiration!! I'll work it out!!
 
Ok. Thanks for all your advice. It's very much appreciated. I've just been reading through the WPD paperwork and it specifies that "The tails should be Tri-rated cable" Does anyone know if SWA is classed as Tri-rated?
Mark if they are fitting a CT chamber are you sure the Tri rated is not just from the CTs to the meter?
 

Reply to Running of distribution cables in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
351
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
313
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
367

Similar threads

See there is the problem. I can put back to way it was. Is it safe, in my opinion NO!! It's wasn't safe before the incident. No Fused Spur...
Replies
9
Views
474
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
2
Replies
21
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top