Hi guys,

I am just trying to price a job up, which I am a bit unsure of. It is at a commercial premises, the supply I have got is 300a three phase, with ruffley 150a - 200a per phase already being used. The customer has asked me to run a supply, 300m (buried) for a 50kw load. It will supply staff living quarters, like a three storey house, and also possible expention in the future.
I have calculated the cable to 70mm2 SWA, 4core, with a 50mm2 earth. Do you think I should still put a earth rod in at the load side, house side?
Also a bit in unsure on protection, I calculated 125a 60947-2?
And then I was thinking of splitting the phases for each floor at the house, so ground floor L1, 1st floor L2 + 2nd floor L3?
Any help will me much appreciated
 
What ever size cable it doesn’t matter. By asking on here you show you’re out of your depth completely. How did you get to quote for this job?
 
Just a warning mate. If you are qualified, but presumably working for someone else atm, do you have public liability in place just in case something were to go wrong?
 
Kibble, I know nothing about 3-phase but I know if I were to use one phase for each floor of a dwelling then I would have 400v between Lines in the ceiling.

Laurie
 

Reply to Running of SWA, sub main in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
838
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top