Hi guys,
I am just trying to price a job up, which I am a bit unsure of. It is at a commercial premises, the supply I have got is 300a three phase, with ruffley 150a - 200a per phase already being used. The customer has asked me to run a supply, 300m (buried) for a 50kw load. It will supply staff living quarters, like a three storey house, and also possible expention in the future.
I have calculated the cable to 70mm2 SWA, 4core, with a 50mm2 earth. Do you think I should still put a earth rod in at the load side, house side?
Also a bit in unsure on protection, I calculated 125a 60947-2?
And then I was thinking of splitting the phases for each floor at the house, so ground floor L1, 1st floor L2 + 2nd floor L3?
Any help will me much appreciated
Whats the earth rod for?? is it a TT installation? and if you ran a new submain in the new DB would be TNS...... you need to work out the load on the new Db, amount of sockets, lights etc, the diversity, to design a building you work back from the power required, that determines the size of board needed, which determines the size of cable feeding it, once you have that, then you will look at spare capacity in the existing board, and 3 phase installations are not designed by simply throwing one phase per floor!! you will need to balance the phases, which means looking at which parts will be used the most, and if you have say 2 socket circuits within touching distance they need to be on the same phase, and lights, if you have 2 way lighting for example with 2 circuits in the switch, again, same phase, all the while thinking about the same load being on each phase, protection - if it was me the new submain would be 100mA protected, then drop to 30mA for sockets etc... housebashing it aint.... regs will give you the cable sizes needed, dont forget grouping factor, (if needed) derating factor for ambient temp, (if needed), and volt drop, if you are using SWA - eland cables website do great easy to follow data sheets,
like i said you will have to work back, if the guy wants a price then a true price would involve 1- 2 days design on the new building just to work out the power requirement.....