Hoping to install (if things get back to normalish) a Ryefield board on a job soon. Haven’t installed one before, according to the drawing from UKPN, the meters will be after the ryefield board - will the suppliers do their own tails into the ryefield board or will I have to supply that? Seems a bit of a grey area..
The DNO will give you a head and then that is it. Once the installation is complete then you can apply the the meters. All the Ryfield Board and sub-mains must be carried out by the electrical contractor.
The dno will request an isolator before the ryefield aswell, also there will be a pme link inside the ryefield (factory fitted ) this needs to be removed if there is to be pme at the head.
[ElectriciansForums.net] Ryefield board
Not the best picture, its installed in a dark basement with other scruffy services but anyway heres one I'm working on. The small enclosure above the Ryfield houses a SPD. Which is fused from the Ryfield unit. I'm going to add an indicator light to the passive relay on the SPD before its finished..
[automerge]1586209405[/automerge]
@sponge23
Check out page 14 for trunking and tail sizes.
  • UKPowerNetworks_Site-Information-Pack_V2Dec2017_FINAL.pdf
@sponge23
Thanks mate. Nice neat job that!
Reply to Ryefield board in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Ask your electrician when they do a site visit as to what is required they can also notify the installation to Building Control under Part P of...
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...