Hoping to install (if things get back to normalish) a Ryefield board on a job soon. Haven’t installed one before, according to the drawing from UKPN, the meters will be after the ryefield board - will the suppliers do their own tails into the ryefield board or will I have to supply that? Seems a bit of a grey area..
 
The DNO will give you a head and then that is it. Once the installation is complete then you can apply the the meters. All the Ryfield Board and sub-mains must be carried out by the electrical contractor.
 
The dno will request an isolator before the ryefield aswell, also there will be a pme link inside the ryefield (factory fitted ) this needs to be removed if there is to be pme at the head.
 
[ElectriciansForums.net] Ryefield board
Not the best picture, its installed in a dark basement with other scruffy services but anyway heres one I'm working on. The small enclosure above the Ryfield houses a SPD. Which is fused from the Ryfield unit. I'm going to add an indicator light to the passive relay on the SPD before its finished..
[automerge]1586209405[/automerge]
@sponge23
Check out page 14 for trunking and tail sizes.
 

Attachments

  • UKPowerNetworks_Site-Information-Pack_V2Dec2017_FINAL.pdf
    4 MB · Views: 28
Last edited:
View attachment 57099
Not the best picture, its installed in a dark basement with other scruffy services but anyway heres one I'm working on. The small enclosure above the Ryfield houses a SPD. Which is fused from the Ryfield unit. I'm going to add an indicator light to the passive relay on the SPD before its finished..
[automerge]1586209405[/automerge]
@sponge23
Check out page 14 for trunking and tail sizes.
Thanks mate. Nice neat job that!
 

Reply to Ryefield board in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Ask your electrician when they do a site visit as to what is required they can also notify the installation to Building Control under Part P of...
Replies
1
Views
460
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top