F

feebs73

help!!
I am working with a made plumber, he has installed a S PLAN SYSTEM, but with a diverter valve ( witch is a two port eebszone valve ) near the cylinder. so in total there are 3 zone valves apparently this gets wired to the cylinder stat???
cant find any wiring diagrams to follow, they all say two zone valves not 3?
many thanks
feebs73
 
He also said, this is the new way it is to be done, but I am struggling to find any info on it? Any help would be most appreciated.
 
help!!
I am working with a made plumber, he has installed a S PLAN SYSTEM, but with a diverter valve ( witch is a two port eebszone valve ) near the cylinder. so in total there are 3 zone valves apparently this gets wired to the cylinder stat???
cant find any wiring diagrams to follow, they all say two zone valves not 3?
many thanks
feebs73


"Hello feebs73",

Please don`t be offended by the `Tone` of this message - I am trying to prevent You getting into a VERY Serious situation.


Please be VERY Careful what You do regarding wiring this Heating and Hot Water System !


IF this Third Zone Valve is installed on the Primary Heating Pipework [Flow and Return] to an Unvented Hot Water Cylinder the following applies:

The additional Zone Valve is part of the `EMERGENCY CUT OFF` Process for an Unvented Hot Water Cylinder it operates in the event of the Cylinder becoming Overheated to prevent Over-pressurisation and possible `Exploding` of the Cylinder IF the Pressure Relief Valve was Faulty.

The Unvented Hot Water Cylinder`s `Safety Zone Valve`is controlled by the EMERGENCY `High Limit Thermostat` on the Unvented Hot Water Cylinder ONLY - Nothing at all to do with the Heating System Controls.


I am a Heating Engineer - But I would not be prepared to advise You on wiring the Zone Valve on this Forum even if I was Electrically Qualified - as it is VITAL that this is done correctly - as will be shown in the Unvented Hot Water Cylinder Installation Instructions.

The Instructions for the Unvented Hot Water Cylinder MUST be followed `to the letter` for wiring the Unvented Cylinder`s Safety Zone Valve.


THIS IS A VERY SERIOUS MATTER - THESE UNVENTED HOT WATER CYLINDERS CAN BECOME `BOMBS` OF RAPIDLY EXPANDING STEAM IF THEY RUPTURE BECAUSE OF BECOMING OVER-PRESSURISED DUE TO OVERHEATING !

IF AN UNVENTED HOT WATER CYLINDER WERE TO OVERHEAT TO ABOVE BOILING POINT [POSSIBLE BECAUSE AT HIGHER PRESSURE THAN ATMOSPHERIC PRESSURE] AND THEN RUPTURE BECAUSE OF THE VAST INCREASE IN PRESSURE THAT COULD OCCUR [IF THE PRESSURE RELIEF VALVE FAILED TO OPERATE] THE RESULT WOULD BE THAT THE WATER WOULD INSTANTLY TURN TO STEAM AND `EXPLODE` / EXPAND RAPIDLY TO 1600 TIMES THE CYLINDER VOLUME !

THIS HAS OCCURRED IN THE PAST DUE TO THE `SAFETY CONTROLS` EITHER NOT BEING FITTED - OR NOT BEING WIRED CORRECTLY - OR A COMBINATION OF BOTH.



Unvented Hot Water Cylinders have at least TWO forms of `Emergency Controls` - these are a Pressure Relief Valve AND an Overheat Protection System - an High Limit Thermostat controlling a `Safety Zone Valve` to prevent Overheating of the Hot Water and Over-pressurisation of the Unvented Cylinder.

If an Immersion Heater is fitted these MUST have a `High Limit` `Cut Off` Thermostat - for the same reason as above - and should be supplied by the Manufacturer of the Unvented Hot Water Cylinder.


I should mention that the Plumber who has installed this System / the Unvented Hot Water Cylinder should be Registered - Trained and Assessed for `Unvented Hot Water Systems` - otherwise He should NOT be Installing them - this is a requirement of the Building Regulations.

If He is `Trained - Assessed and Registered` - He should certainly have been able to let You know that this `Zone Valve` / `Safety Zone Valve` was ONLY to be operated by the Unvented Hot Water Cylinder `High Limit Thermostat` !


And He should have been able to let You read the Installation Instructions regarding the Electrical wiring of the `Overheat Safety Zone Valve` - it would definitely be shown.


Just as a matter of interest could You let Us know what You mean by a `made Plumber` ?



I hope that this is helpful to You and other Members - as I mentioned Please don`t be offended by the tone of My message - I am NOT trying to be pedantic - but this is a VERY serious issue IF the wiring of the `Safety Zone Valve` is not done correctly.


Regards,

Chris - Heating Engineer and Registered Gas Engineer [Plus Registered for Unvented Hot Water Systems].
 
Last edited:
Hi Chris

Fantastic answer to this question, very informative
Cheers Mate


"Hello T&Earth",


Thanks for the compliment - I do try to answer these kind of questions where somewhat `specialised` knowledge of Heating - Gas - Plumbing or in this case Unvented Hot Water Systems is required.

Especially as in this case where there is the potential for a VERY serious situation to be created regarding the `Safety High Limit Thermal Protection` system possibly not being wired correctly.


However I do get a little disappointed when I don`t receive a reply from the person that I am trying to help - especially because I type using only ONE finger and a post such as My one above obviously takes a LONG time for Me to compose and type.


Thanks again.


Regards,


Chris
 
"Hello T&Earth",


Thanks for the compliment - I do try to answer these kind of questions where somewhat `specialised` knowledge of Heating - Gas - Plumbing or in this case Unvented Hot Water Systems is required.

Especially as in this case where there is the potential for a VERY serious situation to be created regarding the `Safety High Limit Thermal Protection` system possibly not being wired correctly.


However I do get a little disappointed when I don`t receive a reply from the person that I am trying to help - especially because I type using only ONE finger and a post such as My one above obviously takes a LONG time for Me to compose and type.


Thanks again.


Regards,


Chris

Don't be disheartened mate, your posts are always really informative, helpful and to the point, it's priceless having you around to help on these kind of questions.

To the OP, I would question the design with the installer and ask him to provide you with a wiring diagram for the system.
 
"Hello feebs73",

Please don`t be offended by the `Tone` of this message - I am trying to prevent You getting into a VERY Serious situation.


Please be VERY Careful what You do regarding wiring this Heating and Hot Water System !


IF this Third Zone Valve is installed on the Primary Heating Pipework [Flow and Return] to an Unvented Hot Water Cylinder the following applies:

The additional Zone Valve is part of the `EMERGENCY CUT OFF` Process for an Unvented Hot Water Cylinder it operates in the event of the Cylinder becoming Overheated to prevent Over-pressurisation and possible `Exploding` of the Cylinder IF the Pressure Relief Valve was Faulty.

The Unvented Hot Water Cylinder`s `Safety Zone Valve`is controlled by the EMERGENCY `High Limit Thermostat` on the Unvented Hot Water Cylinder ONLY - Nothing at all to do with the Heating System Controls.


I am a Heating Engineer - But I would not be prepared to advise You on wiring the Zone Valve on this Forum even if I was Electrically Qualified - as it is VITAL that this is done correctly - as will be shown in the Unvented Hot Water Cylinder Installation Instructions.

The Instructions for the Unvented Hot Water Cylinder MUST be followed `to the letter` for wiring the Unvented Cylinder`s Safety Zone Valve.


THIS IS A VERY SERIOUS MATTER - THESE UNVENTED HOT WATER CYLINDERS CAN BECOME `BOMBS` OF RAPIDLY EXPANDING STEAM IF THEY RUPTURE BECAUSE OF BECOMING OVER-PRESSURISED DUE TO OVERHEATING !

IF AN UNVENTED HOT WATER CYLINDER WERE TO OVERHEAT TO ABOVE BOILING POINT [POSSIBLE BECAUSE AT HIGHER PRESSURE THAN ATMOSPHERIC PRESSURE] AND THEN RUPTURE BECAUSE OF THE VAST INCREASE IN PRESSURE THAT COULD OCCUR [IF THE PRESSURE RELIEF VALVE FAILED TO OPERATE] THE RESULT WOULD BE THAT THE WATER WOULD INSTANTLY TURN TO STEAM AND `EXPLODE` / EXPAND RAPIDLY TO 1600 TIMES THE CYLINDER VOLUME !

THIS HAS OCCURRED IN THE PAST DUE TO THE `SAFETY CONTROLS` EITHER NOT BEING FITTED - OR NOT BEING WIRED CORRECTLY - OR A COMBINATION OF BOTH.



Unvented Hot Water Cylinders have at least TWO forms of `Emergency Controls` - these are a Pressure Relief Valve AND an Overheat Protection System - an High Limit Thermostat controlling a `Safety Zone Valve` to prevent Overheating of the Hot Water and Over-pressurisation of the Unvented Cylinder.

If an Immersion Heater is fitted these MUST have a `High Limit` `Cut Off` Thermostat - for the same reason as above - and should be supplied by the Manufacturer of the Unvented Hot Water Cylinder.


I should mention that the Plumber who has installed this System / the Unvented Hot Water Cylinder should be Registered - Trained and Assessed for `Unvented Hot Water Systems` - otherwise He should NOT be Installing them - this is a requirement of the Building Regulations.

If He is `Trained - Assessed and Registered` - He should certainly have been able to let You know that this `Zone Valve` / `Safety Zone Valve` was ONLY to be operated by the Unvented Hot Water Cylinder `High Limit Thermostat` !


And He should have been able to let You read the Installation Instructions regarding the Electrical wiring of the `Overheat Safety Zone Valve` - it would definitely be shown.


Just as a matter of interest could You let Us know what You mean by a `made Plumber` ?



I hope that this is helpful to You and other Members - as I mentioned Please don`t be offended by the tone of My message - I am NOT trying to be pedantic - but this is a VERY serious issue IF the wiring of the `Safety Zone Valve` is not done correctly.


Regards,

Chris - Heating Engineer and Registered Gas Engineer [Plus Registered for Unvented Hot Water Systems].

Hi Chris
Please accept my appologise, i have been out of reach recently. I have read your reply with much intrest, i did look through the cylinder book but just found a normal wiring diagram nothing about this cylinder cut off valve. i always want to do my job properly so went looking on line asked the plumbers i know, but with no luck.
could you point me in the wright direction where i could find this information as i still have not found this wiring diagram.
Just out of interest has this method been in place long as i am working on two 5 bed 3 ensuites, 1 bathroom, with under floor heating on ground floor, the 1st and 2nd each have a room stat and a zone valve for each floor, but not a cylinder zone valve, is this write??
the "made plumber" should of been "mad plumber" i have fat fingers.

Thank you once again
feebs 73

- - - Updated - - -

"Hello feebs73",

Please don`t be offended by the `Tone` of this message - I am trying to prevent You getting into a VERY Serious situation.


Please be VERY Careful what You do regarding wiring this Heating and Hot Water System !


IF this Third Zone Valve is installed on the Primary Heating Pipework [Flow and Return] to an Unvented Hot Water Cylinder the following applies:

The additional Zone Valve is part of the `EMERGENCY CUT OFF` Process for an Unvented Hot Water Cylinder it operates in the event of the Cylinder becoming Overheated to prevent Over-pressurisation and possible `Exploding` of the Cylinder IF the Pressure Relief Valve was Faulty.

The Unvented Hot Water Cylinder`s `Safety Zone Valve`is controlled by the EMERGENCY `High Limit Thermostat` on the Unvented Hot Water Cylinder ONLY - Nothing at all to do with the Heating System Controls.


I am a Heating Engineer - But I would not be prepared to advise You on wiring the Zone Valve on this Forum even if I was Electrically Qualified - as it is VITAL that this is done correctly - as will be shown in the Unvented Hot Water Cylinder Installation Instructions.

The Instructions for the Unvented Hot Water Cylinder MUST be followed `to the letter` for wiring the Unvented Cylinder`s Safety Zone Valve.


THIS IS A VERY SERIOUS MATTER - THESE UNVENTED HOT WATER CYLINDERS CAN BECOME `BOMBS` OF RAPIDLY EXPANDING STEAM IF THEY RUPTURE BECAUSE OF BECOMING OVER-PRESSURISED DUE TO OVERHEATING !

IF AN UNVENTED HOT WATER CYLINDER WERE TO OVERHEAT TO ABOVE BOILING POINT [POSSIBLE BECAUSE AT HIGHER PRESSURE THAN ATMOSPHERIC PRESSURE] AND THEN RUPTURE BECAUSE OF THE VAST INCREASE IN PRESSURE THAT COULD OCCUR [IF THE PRESSURE RELIEF VALVE FAILED TO OPERATE] THE RESULT WOULD BE THAT THE WATER WOULD INSTANTLY TURN TO STEAM AND `EXPLODE` / EXPAND RAPIDLY TO 1600 TIMES THE CYLINDER VOLUME !

THIS HAS OCCURRED IN THE PAST DUE TO THE `SAFETY CONTROLS` EITHER NOT BEING FITTED - OR NOT BEING WIRED CORRECTLY - OR A COMBINATION OF BOTH.



Unvented Hot Water Cylinders have at least TWO forms of `Emergency Controls` - these are a Pressure Relief Valve AND an Overheat Protection System - an High Limit Thermostat controlling a `Safety Zone Valve` to prevent Overheating of the Hot Water and Over-pressurisation of the Unvented Cylinder.

If an Immersion Heater is fitted these MUST have a `High Limit` `Cut Off` Thermostat - for the same reason as above - and should be supplied by the Manufacturer of the Unvented Hot Water Cylinder.


I should mention that the Plumber who has installed this System / the Unvented Hot Water Cylinder should be Registered - Trained and Assessed for `Unvented Hot Water Systems` - otherwise He should NOT be Installing them - this is a requirement of the Building Regulations.

If He is `Trained - Assessed and Registered` - He should certainly have been able to let You know that this `Zone Valve` / `Safety Zone Valve` was ONLY to be operated by the Unvented Hot Water Cylinder `High Limit Thermostat` !


And He should have been able to let You read the Installation Instructions regarding the Electrical wiring of the `Overheat Safety Zone Valve` - it would definitely be shown.


Just as a matter of interest could You let Us know what You mean by a `made Plumber` ?



I hope that this is helpful to You and other Members - as I mentioned Please don`t be offended by the tone of My message - I am NOT trying to be pedantic - but this is a VERY serious issue IF the wiring of the `Safety Zone Valve` is not done correctly.


Regards,

Chris - Heating Engineer and Registered Gas Engineer [Plus Registered for Unvented Hot Water Systems].

Hi Chris
Please accept my appologise, i have been out of reach recently. I have read your reply with much intrest, i did look through the cylinder book but just found a normal wiring diagram nothing about this cylinder cut off valve. i always want to do my job properly so went looking on line asked the plumbers i know, but with no luck.
could you point me in the wright direction where i could find this information as i still have not found this wiring diagram.
Just out of interest has this method been in place long as i am working on two 5 bed 3 ensuites, 1 bathroom, with under floor heating on ground floor, the 1st and 2nd each have a room stat and a zone valve for each floor, but not a cylinder zone valve, is this write??
the "made plumber" should of been "mad plumber" i have fat fingers.

Thank you once again
feebs 73
 
Hi there
when you say a s plan plus, do you mean an extra zone with a zone valve controlling it?. If that is the case than no it isn't
Many thanks
feebs73
 
Make you mind up, you clearly mention the use of 3 'zone valves' in your opening post.

TBH never heard of an 'eebszone valve'

This 2 port valve near the cylinder is usually for you hot water control, switched by the cylinder stat.

What would this diverter valve be diverting?
 

Reply to s plan central heating 3 zone valves in the Central Heating Systems area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

Unfortunately I don't think you will get an "off the shelf" diagram for the system you are trying to do The Wiser system is very adaptable but it...
Replies
1
Views
469
Multiple zones with S plans I've made work in the past using contactors to do the CFH to the boiler - easy enough. Just think of it all as a...
Replies
1
Views
869

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top