S-Plan central heating - bypass microswitch?
I have Drayton motorised valves for my central Heating and hot water in an S Plan configuration. However, I have had several failures of the microswitches in these valve where they've not switched off and so left the pump and boiler running. This leads to the boiler over heating and so tripping and needing to be reset (imagine if it didn't trip??!!).
So I was wondering of I could bypass these and switch on the pump and boiler directly when the timer/thermostat call for heat? I really don't see any benefit in going via these microswitches.
What about the situation where the valve fails to open. ?
The boiler shouldn't overheat and cause a trip, it should simply shut down either via room stat, immersion stat or internal boiler stat.
But what's the difference between that and the valve closing but the microswitch not switching off?
The boiler does overheat: the valve closes but the microswitch fails, meaning the pump and boiler continue to run, water doesn't circulate but the boiler is burning gas until it overheats and trips. At this point the boiler no longer fires and the pump runs forever against a closed valve. Bonkers!
You need to know that the valve is actually open before the boiler and pump starts.
Generally, the switches are reliable, It may be worth adding a contactor to switch the pump instead of directly from the microswitch.
Is the failing of the micro switches due to contacts fusing together, or is it a mechanical one ?
Is the failing of the micro switches due to contacts fusing together, or is a mechanical one ?
Failure just seems to be a mechanical one.
I realise that the valve is open before the boiler and pump start but they're closed if the micro switch fails. It just seem less likely that the motor or valve will fail than the micro switch, at least in my experience of my one house.
If you bypass the microswitches you'd need to incorporate a couple of contactors or relays to avoid each zone back feeding each other. The microswitches stop this as well as only firing the boiler/pump when the valve is open.
A different solution would be to switch out the brand of valves to another like Danfoss or Honeywell.
Would also be worth considering getting a bypass fitted so that in the event of a similar failure the pump isn't pushing against closed valves.
But if the microswitch fails and doesn't switch off, there is no way of switching off the pump (and boiler but that trips). I can turn down the thermostat/turn off the hot water (depending on which has failed) but the pump will merrily carry on till the cows I don't have come home! That seems utterly bonkers to me.
I have an S plan with 2 zone valves and a Worcester 30cdi combi boiler. The hw water valve was stuck open, which I didn't realise, and the ch valve became sluggish to return from open. We had 2 issues recently where the ch valve stuck in fully open, and the microswitch was operated. I have discovered that unlike the Y plan, the 2 zones have constant 240 at the microswitch, and will send a run command to the boiler, overriding the thermostat etc. This appears to be the way they operate, unlike the Y plan systems. We went away for a few days, with the thermostat set to 16 , but we came back to a baking house as the ch valve had stuck open, the microswitch was operated, and the boiler just kept running at full whack.
I thought I had set the holiday mode incorrectly, and all seemed well after a full power down and restart, but it happened again the other evening and we could not control the heating from the thermostat. At this point I had to apply my diagnostic skills from a different field and worked out the power issue ( Not a real plumber, so had to start from scratch) 2 new valve heads later and all purring and the water isn't scalding either!!
Exactly the point I'm making. The microswitch drives everything so any failure in the system that prevents it from going on/off correctly will mean you can't take control from the thermostat or remotely (if like me you have a Nest thermostat). Imagine if you'd gone away for a couple of weeks (or more!) - boiler running constantly 24 hours a day!!! The wiring has been designed by someone who's just started their wiring design course!
Totally agree
The first time the problem occured was this exact scenario. I had just replaced the ancient rotary thermostat for a new, digital type Honeywell. We went away for a week, and I set it for 16 degrees for 10 days, but we came back to a house at about 25 degrees and the boiler on full. My wife, of course just assumed I'd set it wrong, and we powered the system down so everything would cool down. Respect to the WorcesterBosch 30CDi boiler for just doing its job...On powering up a few hours later the system appeared to be working, but a few days later, whilst we were home, the house started to get very hot again. I then had to don my service engineer hat and work it out.
I'm amazed at such a poor design is normal...my old house had a 3 port valve and the operation is totally different and in 30 plus years I've replaced a few valves and heads, but the house never heated up like this one...
The 3 port valves have their own problems and failure modes - not to mention that they can't zone the heating, and a not insignificant number of people don't fully understand them.
The 2 port valve & S-plan is an elegant design that handles an arbitrary number of zones with simple wiring.
There are ways of avoiding the problems described, but involve adding at least one relay. Instead of connecting grey or orange to live, connect it to the brown so the controls apply power to the microswitch as well as the motor - thus the switch output cannot be live when the controls are off.
However you then need to combine the switched outputs without backfeeding another zone. That's where the relay(s) come in.
They most certainly do, to the extent that I've converted more than a few to S plan over the years.
Depending on whether heating or hot water was used last, the motor in a 3 port valve can remain powered up for months if the system isn't used in the summer, which I'm convinced slowly cooks it.
PedroKTFC,
brianmoooore,
