hi everyone,

When demonstrating safe isolation on the lighting circuit on am2 do you operate the switches and test each time you operate.
Or, just operate the switches in every position then just test once at the 2d light fitting?
Also, when commencing a ZE test would you recommend setting the megger test on a 2 lead high or low. I’m pretty sure I was advised to put it on low. Just want to double check

Cheers
 
for safe isolation of any circuit, you switch off the MCB and lock off. then test with approved voltage tester. L-N , L-E, N-E.

for Ze always use hi current 2 lead.
 
That’s fine. But, just wanted to know if you test at the 2d fitting with the switches in every position e.g three times. Or, just switch the switches in every position to show the light does not come on then test at the fitting once?

I’m just sure I was told to test on low because of the RCBO? May be wrong though
 
If you have safely isolated the lighting circuit (or indeed the whole DB) and then tested at the board that the light circuit outgoing cable is dead and tested at the light fitting that it is dead; then, no matter what switching arrangement you have, any one switch operated should change the state of the lights and a repeat test at the light fitting should cover all possibilities. (Then check to ensure the voltage indicator is still working on the proving unit.)

As there may be an RCD protecting the supply before the test bay use the low current test to test Ze or Zs.
Though Tel is right in general normal practice that Ze, tested at the origin of an installation, should not have an RCD on the supply so a high current test is best.
 
On the test the require you to just isolate the lighting circuit notbtbe whole board. So, identify the breaker turn off and lock off. Then switch switches in all positions, then test at fitting. (Obviously testing voltage tester with proving unit before and after).
They want you to demonstrate working on a one circuit while the rest of the installation remains live
 

Reply to Safe isolation on lighting circuit am2 in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
578
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
764
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

A suitable contactor can be used for safe isolation, but to be suitable it must be marked with the specific symbol for isolation and would have to...
Replies
3
Views
211
Thank you for your response. I really appreciate it.
Replies
13
Views
805

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top