EAWR 1989, Regulation 14a is statutory and absolute (no exceptions) states "No person shall be engaged in any work activity on or near any live conductor (other than one suitably covered with insulating material so as to prevent danger) that danger may arise unless - a) it is unreasonable in all circumstances for it to be dead; and b) it is reasonable in all the circumstances for him to be at work on or near it while it is live; and c) suitable precautions (including where necessary the provision of suitable protective equipment) are taken to prevent injury. Such work is permitted only if conditions a) and b) and c) are satisfied, ‘Work’ is not confined to electrical work but includes any work activity.”
[FONT=&quot]HSE, Guidance Note GS38, conveniently paraphrases the salient points of Regulation 14a, “No live working unless:- (i) it is unreasonable to work dead; AND (ii) it is reasonable to work live; AND (iii) suitable precautions are taken to prevent injury. Live work permitted only if (i) AND (ii) AND (iii) satisfied.
[/FONT]Therefore proving a approved voltage indicators MUST be done on a proving unit (a known voltage source) and NOT on a known LIVE voltage supply (e.g. live side of the isolated main switch, that many electricians mistakenly believe it is acceptable) as this contravenes EAWR 1989 Regulation 14a, the very reason you are required to carry out safe isolation in the first place.
 
Last edited by a moderator:
I know that this thread is being resurrected after almost 2 years, so I apologise.

I just wanted to double-check that for an annual inspection you need to have a separate Voltage Detector with a Proving Unit and you cannot use a Proving Unit with a T5-1000 / Volt Alert etc to evidence safe isolation? If so, I guess I’ll be ordering these tomorrow with a new Lock Out Kit.

Thanks in advance.
 
Do you mean for an elecsa (others avaiable) type annual inspection...if so, you don't need an actual proving unit, aslong as your tester has a built in proving unit which pretty much all do nowadays.
 
I am going to be registering with a scheme provider within the next couple of weeks (before the Part-P regulations / criteria changes), but I am not sure whether my Fluke T5-1000 unit is adequate or whether I need something like the Martindale VI 13700/2 Contact Voltage Detector and Martindale PD440 Proving Unit set - I am thinking of going NICEIC if that makes any difference?
 
google - ESC best practice guide 12 easy steps for isolation, its on page 17, isolation steps. while you are there google - RS - voltage indicator / proving unit, made by martindale, also lock out kit. i must say it amazes me that any electrician in work today does not have basic safety equipment for safe isolation, never mind unsure of how to do it! if i even looked at a supply without an AP written safe system of work in place, a permit and all the right gear i would be down the road!
 
Thanks for the reply. I've always 1st and 2nd fixed new builds, but I'm wanting to go on a register with a scheme, so that I can continue on my way to full competency / qualification status.

In addition, I received this email from the NICEIC today:

"Some time ago you enquired about joining the NICEIC and I thought I would take a minute to go through some of our past enquiries to let you know about some upcoming changes that have been put in place.
As of April 6th 2013, the requirements to join a competent person’s scheme with any of the scheme providers will change. At the moment the only qualification required to join a scheme is a 17th edition. This will be changing to a range of different qualifications depending on what work or experience you have had.

This may mean that you are able to join a scheme at the moment but not be qualified enough to join after the 6th of April.
If you were to make an application to us before April then you would be absolutely fine on just the 17th edition qualification.

The new IET Document that has the changes in can be found here:
http://electrical.------.org/building-regulations/eas/index.cfm"
 

Reply to Safe Isolation! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
625
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
955

Similar threads

View: https://www.youtube.com/watch?v=glsg2HpWyok
2
Replies
21
Views
1K
A suitable contactor can be used for safe isolation, but to be suitable it must be marked with the specific symbol for isolation and would have to...
Replies
3
Views
232

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top