Hi Folks,
Not been on here for a while, but something came up the other day that has me concerned to the point I thought I would ask here.
A good friend asked me if I would connect up a new electric shower for him. This is an older gent, a farmer, and as much I like to look out for him and his wife, I advised him that for safety sake he needs a qualified electrician to do this...
As I was at the house, I agreed to "have a look" with a view to repeating he needs a qualified spark...
The farm house was supposedly rewired about 10 years ago, but I think he got taken for a ride. In this case , looking at the CU, the current shower is fed of a 32amp MCB with 6mm T&E, but at the shower end, the wiring is on the old colour scheme although I think its still 6mm T&E.
The real problem is the shower he intends to buy (or the one his wife wants!) is 12.5Kw. Would that be safe to run off 6mm T&E/32amp MCB?
After my warning, it seems the "plumber" who has been approached to change the shower says as the wiring is already there, he will change it over and it will be "fine"..
I really like the old gent, and I am hoping that I am worrying over nothing, but is 6mm T&E (especially old T&E) enough for the load or should it be upgraded to 10mm?
Thanks in advance,
Peter
(edited power rating of shower to 12.5Kw due to sausage fingers)
Not been on here for a while, but something came up the other day that has me concerned to the point I thought I would ask here.
A good friend asked me if I would connect up a new electric shower for him. This is an older gent, a farmer, and as much I like to look out for him and his wife, I advised him that for safety sake he needs a qualified electrician to do this...
As I was at the house, I agreed to "have a look" with a view to repeating he needs a qualified spark...
The farm house was supposedly rewired about 10 years ago, but I think he got taken for a ride. In this case , looking at the CU, the current shower is fed of a 32amp MCB with 6mm T&E, but at the shower end, the wiring is on the old colour scheme although I think its still 6mm T&E.
The real problem is the shower he intends to buy (or the one his wife wants!) is 12.5Kw. Would that be safe to run off 6mm T&E/32amp MCB?
After my warning, it seems the "plumber" who has been approached to change the shower says as the wiring is already there, he will change it over and it will be "fine"..
I really like the old gent, and I am hoping that I am worrying over nothing, but is 6mm T&E (especially old T&E) enough for the load or should it be upgraded to 10mm?
Thanks in advance,
Peter
(edited power rating of shower to 12.5Kw due to sausage fingers)