joel89

-
Joined
May 24, 2013
Messages
211
Reaction score
14
Location
Barnsley, South Yorkshire
XPSAC3721 | Preventa XPS AC Safety Relay, 230 V ac, 3NO Safety, NC Auxiliary | Schneider Electric

Hi all, the above attached E-STOP safety relay I use regularly use when carrying out panel build upgrades from 1960-70s panels which most of our machines have, anyway my question is. we have a paint plant automated where the paint head goes up and down sprays, it sprays cylinders which run along a track powered by a motor gearbox, then they run into the heating/burners powered by gas solenoid valves. and theres extractors everywhere, there is 4 x seperate panels, (extractors, track, gas burners & paint spray) currently there is e-stops which just go direct to the stop buttons not threw a safety relay, but these only break the track panel circuit so the paint carries on, burners, and extractors I am wanting to know if you can link Safety Relays together, I need to link 3 together to run the control wiring for each panel threw them thus breaking every panel control from the E-Stop circuit



cheers
 
Last edited:
After you have done your assessment and confirmed what you intend to do then you could create a global Safety circuit that monitors all the safety relays in each panel and if any individual section is operated then the global safety relay operates (this keeps each kit seperate), how this interacts with each panel is down to your risk level but generally you have it operate all the safety relays and have all the resets for each panel running through a N/O channel on your global relay. This way the master needs to be reset first then each of the control panels reset. You can leave all the existing wiring as is this way just adding the global safety relay wiring, or remove all E-stops and replace with a common global E-stop.

I would be designing this set-up with care as I assume the fumes could be explosive if they build up, you need to consider what the extraction system needs to be doing in E-Stop situe or even a fire event.
 
Last edited by a moderator:
Kind of as per Darkwood's reply, I wouldn't think the extractors need to be on an emergency stop circuit, presume they won't be sucking anybody inside them.

Are the burners inside a guarded area/furnace with interlocked doors?

Risk assessment is the very first step in this process, anything else without first completing your risk assessment is pointless.
 
Last edited:

Reply to Safety Emergency Stop Relay Schneider XPS-AC in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
315
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
295
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
361

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top