Following a recent report I have had sent to me t was deemed that multi-core SWA doubled up to
supply a single phase piece of equipment, was unsatisfactory for following reasons.
'Poor onsite installation practice may result in increased risk of failure,electric shock or fire'.
See photo.

To me I understand that it is bad practice to not correct size cable on the original install, however what regulation does it no comply with and is it really a C2?

I mean we do it for larger install supplies.
 

Attachments

  • [ElectriciansForums.net] Satisfactory or Unsatisfactory
    Multicore cable.png
    601 KB · Views: 208
I can only imagine that this is the only cable they had at the time of installation and they've used 2 cores the Live, neutral & earth.
they marked it as C2 because they deem unsafe. It's bad practice but is it unsafe for continued use?
 
more detail needed. is it 2 cores for L and 2 cores for N? as in parallel conductors? the cpc may or may not be adequate if it's a single conductor, esp if there's extraneous parts that require bonding.
 
Looks like there are 2 separate circuits within the same multicore cable. Second and fifth (from top) MCBs seem to be using cores within this same cable as line conductors.

Indeed....two circuits,a radial and RFC? Only got the BRB to hand at home,the reg number may be different in the BYB....but 521.7 applies, two or more circuits are permitted in the same cable provided the usual requirements are met in section 528. No code needed as far as I can see.
 
Last edited by a moderator:
Only got the BRB to hand at home,the reg number may be different in the BYB....but 521.7 applies, two or more circuits are permitted in the same cable provided the usual requirements are met in section 528. No code needed as far as I can see.

Yep I'm aware of that reg. I didn't say anything was technically wrong with it, was just trying to determine what the report could have been alluding to. The report statement is so vague it's hard to tell. I couldn't see it was from the doubling of the conductors.
 
Yes...I spotted that it was two separate circuits and not one as stated in the OP....and never thought you were stating that there was anything wrong with the installation method. In fact it looks like a pretty neat job!
 
Only a problem (and obviously not in this case) if the circuits are for VFDs, the 3 cores must be symmetrical to comply with the EMC regulations. So no multi ores like that.

A bit off topic but a useful nugget of info.
 

Reply to Satisfactory or Unsatisfactory in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top