Hi
I have to look at a job to install temporary lighting to a scaffold. Apart from the obvious ie. 110volt, weather proof bulkheads is there anything else I should look out for?
Thanks in advance
Whilst you'll probably want them to be 110V for other reasons, remember that they don't HAVE to be if they're run from an RCD - 704.410.3.10 (ii). You'll also want to earth the scaffold itself.
Maybe i am not reading it correct but hey its good to discuss, 704.410.3.10 A circuit supplying a SOCKET OUTLET with a rated current upto and includding 32a and any other circuit supplying HANDHELD EQUIPMENT
i would see scaffold lighting as fixed equipment?
just a thought
There's nothing really in section 704 that talks specifically about fixed equipment, so I've always worked on the basis that if it's connected via a plug/socket arrangement (as per the vast majority of onsite kit) then it's best classed as a socket outlet - as it is, isn't it?
But, in fairness Note 1. to the reg does go on to say that reduced low voltage is the preferred option for local lighting up to 2kW.
Totally with you i always back everything up with RCD as due course i was just questioning the regs wording,
Hi
I have to look at a job to install temporary lighting to a scaffold. Apart from the obvious ie. 110volt, weather proof bulkheads is there anything else I should look out for?
Thanks in advance
Where would you like to start picking the 464 pages apart from? We'll need a VERY large pot of coffee, some provisions and a barrel of beer. And probably a masseuse for after.
On many larger sites, there is a requirement for emergency lighting to scaffolds and walkways, may not be relevant here but worth thinking about.
If the two halves of the scaffolding are separated by wooden panels, you can use the front scaffold poles as the live, then the back as the neutral/earth.
Saves a lot of wire.