Hi

I have to look at a job to install temporary lighting to a scaffold. Apart from the obvious ie. 110volt, weather proof bulkheads is there anything else I should look out for?

Thanks in advance
 
Hi

I have to look at a job to install temporary lighting to a scaffold. Apart from the obvious ie. 110volt, weather proof bulkheads is there anything else I should look out for?

Thanks in advance

In my experiance put them up out of reach to stop vandals and if you have any scaffold crossovers/gantrys you may need general lighting as well
 
Whilst you'll probably want them to be 110V for other reasons, remember that they don't HAVE to be if they're run from an RCD - 704.410.3.10 (ii). You'll also want to earth the scaffold itself.
 
Whilst you'll probably want them to be 110V for other reasons, remember that they don't HAVE to be if they're run from an RCD - 704.410.3.10 (ii). You'll also want to earth the scaffold itself.

Maybe i am not reading it correct but hey its good to discuss, 704.410.3.10 A circuit supplying a SOCKET OUTLET with a rated current upto and includding 32a and any other circuit supplying HANDHELD EQUIPMENT

i would see scaffold lighting as fixed equipment?

just a thought
 
110v flourys as said already be mindfull of crossings Loading bays ect where additional lighting may be required Vandals are an obvious thing Check with main contractor re scaffold moves might mean more cable but may also save you getting called everytime they move a bit with a cable on due to scaffolders inability to undo or cut tywraps without ripping the cable ends from fittings first
also bear in mind the test and inspection 3monthly as this is classed as temporary installation even if its going to be up for 10 years
 
Maybe i am not reading it correct but hey its good to discuss, 704.410.3.10 A circuit supplying a SOCKET OUTLET with a rated current upto and includding 32a and any other circuit supplying HANDHELD EQUIPMENT

i would see scaffold lighting as fixed equipment?



just a thought

There's nothing really in section 704 that talks specifically about fixed equipment, so I've always worked on the basis that if it's connected via a plug/socket arrangement (as per the vast majority of onsite kit) then it's best classed as a socket outlet - as it is, isn't it?

But, in fairness Note 1. to the reg does go on to say that reduced low voltage is the preferred option for local lighting up to 2kW.
 
There's nothing really in section 704 that talks specifically about fixed equipment, so I've always worked on the basis that if it's connected via a plug/socket arrangement (as per the vast majority of onsite kit) then it's best classed as a socket outlet - as it is, isn't it?

But, in fairness Note 1. to the reg does go on to say that reduced low voltage is the preferred option for local lighting up to 2kW.


Totally with you i always back everything up with RCD as due course i was just questioning the regs wording,
 
Totally with you i always back everything up with RCD as due course i was just questioning the regs wording,

Where would you like to start picking the 464 pages apart from? We'll need a VERY large pot of coffee, some provisions and a barrel of beer. And probably a masseuse for after.
 
Hi

I have to look at a job to install temporary lighting to a scaffold. Apart from the obvious ie. 110volt, weather proof bulkheads is there anything else I should look out for?

Thanks in advance

On many larger sites, there is a requirement for emergency lighting to scaffolds and walkways, may not be relevant here but worth thinking about.
 
One requirement when I wired lights on scaffolds was that the bulkheads at either end were red while the bulkheads in between were white. All wires cable tied to the under side of the tube. All RCD protected.
 
If the two halves of the scaffolding are separated by wooden panels, you can use the front scaffold poles as the live, then the back as the neutral/earth.

Saves a lot of wire.
 
emergencys would be worth a look DONT put the cables through scaff poles iv seen this done numerous times

there is 110v led ropelighting on the market we "trialed " it on a big project as they were looking for the greenest stuff it was ok for scaffold and great for stairs but not much cop in open areas as the LEDs werent bright enough
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
scaffold lighting
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
16
Unsolved
--

Advert

Thread statistics

Created
lurch,
Last reply from
mogga,
Replies
16
Views
10,230

Advert

Back
Top