Scenario where lack of supplementary bonding is dangerous | on ElectriciansForums

Discuss Scenario where lack of supplementary bonding is dangerous in the UK Electrical Forum area at ElectriciansForums.net

Joined
Nov 2, 2023
Messages
14
Reaction score
2
Location
Coventry
So I know why it is done, where it is done and how it’s done, but I’m yet to see a scenario where there is shock danger in a typical bathroom in a dwelling provided a) the main bonding is in place and b) the CPC’s of all circuits are connected together in the CU (as they will be).

Consensus is on an EICR code 2 where there is no RCD for additional protection and supplementary bonding is not in place. What is the potential danger ? What am I missing ?
 
I usually find that 415.2.2 is satisfied without supplementary bonding being in place in/around the bathroom.
As I said I know why and how it is done and I should have stated where it is not required- I.e where the circuits in the bathroom have additional protection from a 30mA RCD but my question was, and remains, where supplementary bonding is required, what danger exists where it is omitted, assuming all circuits have CpC and main bonding it in place ?
 
where supplementary bonding is required, what danger exists where it is omitted, assuming all circuits have CpC and main bonding it in place ?
Well the assumption is really the point....
One example, someone DIY changes a light fitting with one they got from Ikea and doesn't connect the CPC's properly. Every light after it now has no CPC.
It's then possible to have two different versions of "earth" in the bathroom if someone touches a metal light fitting and an electric towel rail at the same time.
Supplementary bonding is belt and braces making sure that whatever else happens, they all have the same zero potential between them.

At least, that's my take on it. It's an interesting question.
 
Well the assumption is really the point....
One example, someone DIY changes a light fitting with one they got from Ikea and doesn't connect the CPC's properly. Every light after it now has no CPC.
It's then possible to have two different versions of "earth" in the bathroom if someone touches a metal light fitting and an electric towel rail at the same time.
Supplementary bonding is belt and braces making sure that whatever else happens, they all have the same zero potential between them.

At least, that's my take on it. It's an interesting question.
It’s a reasoned response however if the metal light fitting is not earthed then touching it will not be introducing any potential will it ? If it’s faulty with a live/earth fault then yes it (metal parts of the luminaire) will be at 240v buts that’s already covered under the requirement to have a cpc connected to class 1 fittings or the use of class 2 where no cpc ?
 
It’s a reasoned response however if the metal light fitting is not earthed then touching it will not be introducing any potential will it ? If it’s faulty with a live/earth fault then yes it (metal parts of the luminaire) will be at 240v buts that’s already covered under the requirement to have a cpc connected to class 1 fittings or the use of class 2 where no cpc ?
The thing is, it's 'supplementary'. It's additional protection. It's an extra safety net. We could say there's no need for all sorts of things if everything is installed perfectly and maintained perfectly.

We also need to remember that it pre-dates RCDs and it was the best way at the time to make sure that you can never have two pieces of exposed metalwork in a bathroom at different potentials to each other, when the resistance of the body is at an all time low as it's soaking wet.

It has a further role of adding possible earth paths so a phase to earth fault in any circuit in the room will cause ADS even if the faulting circuit has no upstream CPC continuity.

e.g. In the example I gave above, suppose they then like their Ikea light and install another one beyond the bathroom fitting but their twist and tape joint ends up touching the casing and the casing ends up live.
They'll turn the power back on and be none the wiser, but there's no fault protection and it's sitting there with a live case.

However in this case supplementary bonding saves the day and we'll get ADS. Without it, it will still sit there live.

Don't get me wrong, I prefer making sure every circuit in the room is RCD protected.
But I wouldn't say that supplementary bonding is pointless.
 
The thing is, it's 'supplementary'. It's additional protection. It's an extra safety net. We could say there's no need for all sorts of things if everything is installed perfectly and maintained perfectly.

We also need to remember that it pre-dates RCDs and it was the best way at the time to make sure that you can never have two pieces of exposed metalwork in a bathroom at different potentials to each other, when the resistance of the body is at an all time low as it's soaking wet.

It has a further role of adding possible earth paths so a phase to earth fault in any circuit in the room will cause ADS even if the faulting circuit has no upstream CPC continuity.

e.g. In the example I gave above, suppose they then like their Ikea light and install another one beyond the bathroom fitting but their twist and tape joint ends up touching the casing and the casing ends up live.
They'll turn the power back on and be none the wiser, but there's no fault protection and it's sitting there with a live case.

However in this case supplementary bonding saves the day and we'll get ADS. Without it, it will still sit there live.

Don't get me wrong, I prefer making sure every circuit in the room is RCD protected.
But I wouldn't say that supplementary bonding is pointless.
Unless the metalwork of the light fitting in your scenario above is actually earthed (to a cpc) then your supplementary bonding is going to make no difference whatsoever. And if it is earthed it will be at the same potential as all the other circuit Cpcs because they are all connected at the CU - which will be in close proximity to the bathroom , even in a mansion house the potential difference due to circuit length would be in the ELV class
 
You've missed the key point - CPCs not connected to the MET due to a failure (e.g. the dodgy diy).
In an ideal world we'd not have O/C CPCs and all manner of other faults. But in the real world I would suggest that the JPEL64 committee decided there was evidence of sufficient faults to justify having additional protection.
 
Going right back to the beginning:
I’m yet to see a scenario where there is shock danger in a typical bathroom in a dwelling provided a) the main bonding is in place and b) the CPC’s of all circuits are connected together in the CU
I agree with you that if everything is perfect, it is indeed supplementary, the clue is somewhat in the name!
Unless the metalwork of the light fitting in your scenario above is actually earthed (to a cpc) then your supplementary bonding is going to make no difference whatsoever
We seem to agree that everything isn't always perfectly installed.
And if it is earthed it will be at the same potential as all the other circuit Cpcs because they are all connected at the CU
In my scenario this isn't in fact the case as the CPC is broken by the first Ikea light upstream.

CU - Lighting circuit - break in cpc - bathroom light - cpc intact - (multiple lights) - live - earth fault
With SB from bathroom light you get ADS as there is a path from the fault to the CU
Without SB you don't and you have an especially dangerous situation in bathroom and a dangerous situation at final light.

If it isn't earthed, as you suggest:
CU - Lighting circuit - break in cpc - bathroom light - cpc broken - live - earth fault
Yes, SB is irrelevant in this case, but you also don't have a dangerous situation in the bathroom which is what the SB is trying to achieve.

Let's not argue too much - I was born in Coventry too.... ;-)
 
Going right back to the beginning:

I agree with you that if everything is perfect, it is indeed supplementary, the clue is somewhat in the name!

We seem to agree that everything isn't always perfectly installed.

In my scenario this isn't in fact the case as the CPC is broken by the first Ikea light upstream.

CU - Lighting circuit - break in cpc - bathroom light - cpc intact - (multiple lights) - live - earth fault
With SB from bathroom light you get ADS as there is a path from the fault to the CU
Without SB you don't and you have an especially dangerous situation in bathroom and a dangerous situation at final light.

If it isn't earthed, as you suggest:
CU - Lighting circuit - break in cpc - bathroom light - cpc broken - live - earth fault
Yes, SB is irrelevant in this case, but you also don't have a dangerous situation in the bathroom which is what the SB is trying to achieve.

Let's not argue too much - I was born in Coventry too.... ;-)
Hey I’m not arguing and thanks you’ve clarified your scenario which I can see is a valid case and one I hadn’t thought of - in effect loss of a cpc to a class 1 accessory. If then a second fault occurs (making the metalwork live) then ADS will disconnect the circuit removing shock hazard. This is a new one to me thanks because it’s normally stated to do with voltages between extraneous conductive parts. I suspect this scenario is welcome byproduct but not the intended aim ? Because this risk is not made any greater by being in a zone, it could apply to any room couldn’t it and we’d end up supplementary bonding every room in the house ?
 
Last edited:
@Falkus and others, out of interest how would you code this one that I’m about to do:

Small flat. 2 circuits have no rcd protection, lighting and immersion.
Someone has added an electric shower (obvious addition) and there’s no SB.

Normally I would C3 the lighting without RCD.
The bathroom light needs changing anyway as it isn’t IP rated.
If the light is the only other circuit in the room and will be class 2, I’m wavering on C3 for the lack of SB as in this case to my thinking there are too many what-if’s to warrant a C2.

Even though I see the point of SB in this particular case I’m struggling to see a compelling danger as you can’t touch anything else that is class 1.

Would you do the same?
 
@Falkus and others, out of interest how would you code this one that I’m about to do:

Small flat. 2 circuits have no rcd protection, lighting and immersion.
Someone has added an electric shower (obvious addition) and there’s no SB.

Normally I would C3 the lighting without RCD.
The bathroom light needs changing anyway as it isn’t IP rated.
If the light is the only other circuit in the room and will be class 2, I’m wavering on C3 for the lack of SB as in this case to my thinking there are too many what-if’s to warrant a C2.

Even though I see the point of SB in this particular case I’m struggling to see a compelling danger as you can’t touch anything else that is class 1.

Would you do the same?
Well firstly (assuming this is an EICR that you are about to “do”) I would code the EICR on what is the “now” situation not what it will be after you have changed the light or other remediation. Secondly this is the bit I’m trying to rationalise myself because if it’s a C3 then there is no danger or potential danger which would imply supplementary bonding has no bearing on the installation being satisfactory for continued use.
 
@Falkus and others, out of interest how would you code this one that I’m about to do:

Small flat. 2 circuits have no rcd protection, lighting and immersion.
Someone has added an electric shower (obvious addition) and there’s no SB.

Normally I would C3 the lighting without RCD.
The bathroom light needs changing anyway as it isn’t IP rated.
If the light is the only other circuit in the room and will be class 2, I’m wavering on C3 for the lack of SB as in this case to my thinking there are too many what-if’s to warrant a C2.

Even though I see the point of SB in this particular case I’m struggling to see a compelling danger as you can’t touch anything else that is class 1.

Would you do the same?
Can pipework be touched at the same time as the shower?

Edit: I usually just C2 a shower without RCD protection, based on MI's
 
Can pipework be touched at the same time as the shower?
I meant to cover that, in this case answer is no. Shower feed is plastic through the back, the only thing that came close was the bath taps but I checked and that has plastic plumbing too. Sink has a copper cold pipe but is completely out of reach (and also behind the pedestal)
 
This is a new one to me thanks because it’s normally stated to do with voltages between extraneous conductive parts. I suspect this scenario is welcome byproduct but not the intended aim
I think in the broad sense the aim is indeed to ensure there is no potential difference between two things you can touch when you are soaking wet. Whether that is two versions of 'earth' or 'earth' and 230v to my thinking the same principle applies.
Well firstly (assuming this is an EICR that you are about to “do”) I would code the EICR on what is the “now” situation not what it will be after you have changed the light or other remediation
I take your point and many would do that. I have a working relationship with this letting agency that minor things I 'just fix'. A real bug bear of mine is an unsatisfactory EICR because there's a sticker missing on the consumer unit! I honestly think it works better for everyone to just resolve things that are easily resolvable.
Secondly this is the bit I’m trying to rationalise myself because if it’s a C3 then there is no danger or potential danger which would imply supplementary bonding has no bearing on the installation being satisfactory for continued use.
I think we have to look at each case on it's own merits.
If there was a radiator, or a heated towel rail, or anything else with exposed or extraneous conductive parts I wouldn't be suggesting this. In this case the supplementary bonding would be between a shower, a class 2 light fitting and a class 2 extractor fan. So it honestly doesn't really do a lot!
 

Reply to Scenario where lack of supplementary bonding is dangerous in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top