Thank you for educating me regarding the NICEIC test sheets.
I was unaware that the NICEIC procedures varied so greatly to those set out in BS7671, which requires the readings to be adjusted accordingly when testing conductors at a different temperature to their normal operating temperature.
eic max permitted by bs 7671 blank box underneath which you either mark 80 or 100 % which ever you wish to use
but mw 80% max zs
i always use 80%
Reply to Schedule for a db in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
As long as the heat input is greater than the heat losses from the container and the resistance is sufficient to limit the current to no more than...