On a couple of recent EICRs I've run into FCUs on a RFC, then 1.5 or 1mm to several lighting points and would be interested how people would note this on the schedule?
On the most recent one there are 6 outside lanterns fed from an FCU on the socket circuit, with max R1+R2 outside of 4.5Ohm (Dodgy joints partly to blame I suspect, but didn't have time to further investigate).
Putting it as the highest reading on the main RFC circuit doesn't make it clear that there isn't a very poor connection on the sockets that should be investigated. It would also look as though the RCD is being used for fault protection on that circuit without further clarification.
Would you note the fused circuit as a separate circuit in the schedule list, noting 1362 as the OCPD (which means it's well under the 15.6 max Zs). If so, how do you make it clear which circuit it's fed from? I'm thinking of just listing it as "FCU Garden Lights fed from circuit x" - Seems overkill to consider it as another db with a second page of test results just for a fused spur.
On the most recent one there are 6 outside lanterns fed from an FCU on the socket circuit, with max R1+R2 outside of 4.5Ohm (Dodgy joints partly to blame I suspect, but didn't have time to further investigate).
Putting it as the highest reading on the main RFC circuit doesn't make it clear that there isn't a very poor connection on the sockets that should be investigated. It would also look as though the RCD is being used for fault protection on that circuit without further clarification.
Would you note the fused circuit as a separate circuit in the schedule list, noting 1362 as the OCPD (which means it's well under the 15.6 max Zs). If so, how do you make it clear which circuit it's fed from? I'm thinking of just listing it as "FCU Garden Lights fed from circuit x" - Seems overkill to consider it as another db with a second page of test results just for a fused spur.