Can I connect the meter tails into the top of this MCB and the load cable (SWA) out of the bottom. The MCB is not marked for in and out and I cannot find any info on Schneider's web site indicating this is not possible.
 

Attachments

  • [ElectriciansForums.net] Schneider C60HB 3 pole 63A MCB
    MCB_Connect.jpg
    68.1 KB · Views: 47
That's the right way anyway or can I just not see the picture properly?

In a consumer unit the supply comes in the bottom via busbar and the the circuits are connected in the top. At the main isolator, the meter tails are indeed connected into the top. The main switch in this case is going to be in the DNO's panel. I am just installing the MCB to provide short/overload protection up to the house. The 25 mm SWA cable would be better coming out of the bottom as it is quite stiff. Would not be the end of the world if it does have to come out of the top. There will be enough room in the enclosure.
 
Does it matter which way you put them in, either way it will switch the power on and off at the opposite side of the supply terminal.

If that makes sense :s

it makes sense and I know it doesn't matter but just pointing out the top is the supply side

- - - Updated - - -

The tails are coming out of the meter in DNO's enclosure, to my enclosure, through MCB, then SWA to house 25m away.
So the top is the supply
 
1 3 5 connections
I have a bog standard MK B16. This sits on the busbar, so the supply side is coming in the bottom. The circuit is then connected in the top of this CB. The small diagram (numbered on the the Schneider) is not numbered on the MK but is identical in other respects. So the 1,2,3 numbering info was helpful, even though it probably does not matter.
 
Hi,

Probably not the way things are done now, but I was always taught and still do it now, supply in the bottom terminals and load out the top. Either way though and the isolator/switch will still operate correctly.

Regards.
 

Reply to Schneider C60HB 3 pole 63A MCB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
636
  • Question
This charger doesn't support rear entry from the looks, only bottom entry, hence that. Unless they make a white sheathed SWA, I would still need...
Replies
8
Views
963
  • Question
Why not fit a self contained SPD fed directly from the Henley blocks, and free up a bay? Could probably make one up from whats there, using a...
2
Replies
47
Views
4K
  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
642
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
663

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks