B
Discuss Schneider C60HB 3 pole 63A MCB in the UK Electrical Forum area at ElectriciansForums.net
That's the right way anyway or can I just not see the picture properly?
Thanks for that, I thought that might be the caseThe clue is on the front,,1,3,5, in.
With the internal contacts on 2,4,6. not live when off.
But in reality it makes no difference which way round it's connected.
The tails are coming out of the meter in DNO's enclosure, to my enclosure, through MCB, then SWA to house 25m away.I'm so confused what are you using as the supply the tails or the armoured? The top as the supply is the right way round
Does it matter which way you put them in, either way it will switch the power on and off at the opposite side of the supply terminal.
If that makes sense :s
So the top is the supplyThe tails are coming out of the meter in DNO's enclosure, to my enclosure, through MCB, then SWA to house 25m away.
Yes, it does make sense to me, contactors behave this way so it shouldn't really matter. Thanks for that.Does it matter which way you put them in, either way it will switch the power on and off at the opposite side of the supply terminal.
I have a bog standard MK B16. This sits on the busbar, so the supply side is coming in the bottom. The circuit is then connected in the top of this CB. The small diagram (numbered on the the Schneider) is not numbered on the MK but is identical in other respects. So the 1,2,3 numbering info was helpful, even though it probably does not matter.1 3 5 connections
Reply to Schneider C60HB 3 pole 63A MCB in the UK Electrical Forum area at ElectriciansForums.net