Davesparks sound advice however can you always trust previous test results? Especially if it's done by some other company of which you know nothing about.
Fair enoughAgreed MDJ it is whatever the customer wants and that is what the limitations sections are for but as I say in my experience it's a circuit that is left for thirty years after the initial install without a test. Just not worth it mate
I've stated the deal we have in place and it's actually with the local authority which covers 6 schools and two leisure centres. We test it all as an arse covering exercise. Canny do night shift cos it's dark doesn't quite cut it these days
UNG the schools are left in a midden for us to take over and trying to get them back on a snag issue is an interesting conversation. It's just not worth not testing it and leaving it for thirty years after the initial install.
ipf as your post says chances are it will be fine but you're relying on the install guys there and as you say IF a circuit has been installed properly. Personally I'm not relying on them possibly installing it properly.
but do you test every socket?I would test every circuit but may only open a few sockets switches and lights on eachcircuit . I wouldnt open every socket and light fitting if the viewed ones looked good. As long as test are ok!
thanks guys
I would test every circuit but may only open a few sockets switches and lights on eachcircuit . I wouldnt open every socket and light fitting if the viewed ones looked good. As long as test are ok!
thanks guys
then he is not testing 100% as he agreed with client.So you are applying a limitation then
then he is not testing 100% as he agreed with client.
forgive me if Im wrong but doesnt an eicr also state a function test?
How can you perform a function test if you dont check all spckets and it takes no extra time to do r1+r2 then zs at each socket.
(use plug in tester rather than taking fronts off)
I will hold my hand up and say with this firm we have never done a 100% test and inspection.So you are still not inspecting 100% how does a plug in tester check the integrity and tightness of the terminals at a socket
It is very easy to spout about doing a 100% I & T but I'm begining to wonder if people have different interpretations of 100%
There always will on every I & T be some compromise as to completely 100% check one RFC with 20 sockets on would take some time on a large site with a few RFC's of similar size how many circuits are you going to I & T in a day as the customer watches the costs spiral
Yes all sockets would be checked but not opened. A plug in tester would be used. Would you open every light to check connections if the last fitting has good connections?
what about stage lighting multicore swa. Would all of this need testing there is. 4 poles with stage lighting and 15 amp socket outlets all connected to a dimming panel
Davesparks sound advice however can you always trust previous test results? Especially if it's done by some other company of which you know nothing about.
the problem is more people selling the service as a 100% test which missing bits out isntGo on then, how do you go about testing the stage lighting installation?
How do you carry out a Zs test on a hardwired dimmer? Or a patch able system for that matter?
Bearing in mind stage lighting installations for everything from school halls to Glastonbury festival are my specialist subject![]()
I was going to ask about the stage lx installs earlier on but got distracted. You can't do the standard tests out of the book as the dimmer effectively forms a DB (24 ways of dimming at 10A each) but each way is controlled by a dimmer so you can't just plug a loop impedance tester in the end of it and get a sensible result!
But then some testing wombles will code the whole lot C2 due to it having 'obsolete' plugs and sockets! We use 15A round pin sockets to distinguish dimmer controlled sockets from regular sockets.
100 circuits about 3 days work in a empty school, depending on the condition of it
You test the multicore and the plugs and sockets each end of it for all the normal dead tests - unplugged from any dimming - and do not even think about doing any live tests as even if you don't manage to destroy something then the results will be meaningless anyway.
4 ccts per hour over an 8-9 hour day onsite. If school was empty. 100%visual to every accessory 20%removal of accessories on circuit. And the use of common sense
So you would remove every accessory on a large ring main?
100% in a domestic environment is a must but 100% in most commercial building's would be difficult to achieve to a acceptable price and disruption to the client. Previous test results and sufficient sampling of circuits should give anyone a indication to the extant of the test required