B

Ben Burrows

Hi guys, am new to the forum. My issue is I got called to a friends house as they have an issue with their lights, I arrived and the issue was 1 lighting circuit controlling about 5 lights. I only had some hand tools on me thinking it would just be a hidden rcd or a lamp! I played around a little and the rcd trips with only the line conductor connected to the installation and the neutral and cpc isolated(with or without them connected). I think am having a mind blank as cannot think what would cause this to trip. Tried splitting the lights but is an old cottage and there must be jb's under the floor as am missing feeds at lights/switches?If anyone has come across a similar situation or can shed a little "light" on the situation, it would be gratefully received!!!
 
Last edited by a moderator:
My first port of call would be to take a test kit and carry out the sequence of tests on the circuit.

I'd probably then look at breaking down the circuit and testing each half until I found the cause.
 
That is the plan for tomorrow! Just cannot get my head round why it would trip without the neutral or cpc being connected? And also when everything connected will turn lights on for 1-2 seconds and then trip the rcd?
 
the rcd trips with only the line conductor connected to the installation and the neutral and cpc isolated(with or without them connected).

So with the EARTH DISCONNECTED and the LINE STILL connected, there's a fault?
Were there any other people in the house apart from yourself at this time?
 
Supposedly just started this afternoon, no diy etc happening, the rcd just tripped! It made me wonder if there is some water getting in somewhere as we have had a lot of heavy rain today? That's the only thing that has changed, though have checked all the lights, there are outside lights but are on another circuit and are all working?
 
NEVER, and I mean NEVER, energise a circuit with the cpc or neutral disconnected.
I would strongly recommend that your friend employs a competent tradesman who understands the basics of electrical safety.
 

Reply to Scratching my head lighting fault??? in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
558
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
993
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
924

Similar threads

Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
952
Update. Went back today as it was popping the other RCD post move, again intermittently with no real pattern. Typically overnight but not every...
Replies
6
Views
327

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top