Good evening all, I have a query regarding an immersion tank.

I received a call from a new client asking do I fix immersion tanks to which I told her it’s probably best to get a plumber out as he can eliminate the problem and change the element if required which would save her money.

I won’t go into too much detail but it turns out the plumber just changed the immersion element and billed her, the next day later she called me saying that it’s not working again, could I pop over?

After taking a look I soon realised that the timer was an old rotary time guard which isn’t ideal as it hasn’t got a boost function and which had also malfunctioned resulting in a previous DIYer bypassing it resulting in the immersion running 24hrs a day. (This has since been upgraded)

I tested the mains in at the tank which had voltage then nothing coming out of the thermal cut out which I reset then supplying voltage to the element (Could here it heating) I then assured her I had sorted the problem as I had changed the time clock and reset the thermal cut out.

I received another phone call the following day saying it’d stopped working yet again.The only thing left do was to change the thermal cut out for a new one which I did and it worked for 3 days only to trip again today!

I have done way more than I would normally do and this job has cost me money!, I’ve since walked away from the job on good terms explaining to the client I can’t do anything else. In 20 years of doing this I am dumbfounded!

Any ideas on possible causes? I had made sure the thermal cut out was set no higher to 65 degrees? It is an electric only flat with a dual element mega flow type tank although the middle element isn’t being used at all as they don’t have eco7.
 
Last edited:
Nope, the wiring is secure as I double checked everything.

Don’t get me started with the plumber, that’s a whole different topic on its own!

I haven’t got a picture of the gubbins but have a link the thermal stat :


I‘ve done everything I can electrically, maybe there’s a build up of limescale In the tank?, but the plumber would of seen that and commented on it?

As mentioned above, I’m done with the job but never accept defeat! Just wondered if anyone could help me from going insane!
[automerge]1588617003[/automerge]
Guys, I understand how a tank is connected. There really isn’t any use showing a picture as I can assure you it’s all connected properly.

Yes it is an element with spade terminals connected to the stat,
 
Nope, the wiring is secure as I double checked everything.

Don’t get me started with the plumber, that’s a whole different topic on its own!

I haven’t got a picture of the gubbins but have a link the thermal stat :


I‘ve done everything I can electrically, maybe there’s a build up of limescale In the tank?, but the plumber would of seen that and commented on it?

As mentioned above, I’m done with the job but never accept defeat! Just wondered if anyone could help me from going insane!
[automerge]1588617003[/automerge]
Guys, I understand how a tank is connected. There really isn’t any use showing a picture as I can assure you it’s all connected properly.

Yes it is an element with spade terminals connected to the stat,
So which stat do you have then?
 
Nope, the wiring is secure as I double checked everything.

Don’t get me started with the plumber, that’s a whole different topic on its own!

I haven’t got a picture of the gubbins but have a link the thermal stat :


I‘ve done everything I can electrically, maybe there’s a build up of limescale In the tank?, but the plumber would of seen that and commented on it?

I have had that before where the element was caked in lime scale and was sitting on a bed of shingles. As you say though, the plumber would have noticed that.
 
Last edited:
I’ve lost all faith in the plumber, very unprofessional.

I forgot to mention that there is an electric boiler in the cupboard doing the central heating, I don’t think that has anything to do with the problem?

heres a link to the tank :


thanks for all your help.
 
You set the high limit stat to 65 degrees? Is there another dial for actual temperature rather than the high limit temperature?
According to the above attached installer manual it says the element stat is a combined control and overheat stat in the same module. Only the control temperature can be adjusted and it has a range from 10C to 72C.
 

Attachments

  • [ElectriciansForums.net] Scratching my head over immersion heater!
    immstat.png
    87.4 KB · Views: 36
Just a quick update guys,

I’ve just heard back from my client who has informed me that according to her new plumber the thermostat was set too high resulting in nuisance tripping.

I had followed the instructions and set the stat to roughly 65 degrees, I say roughly as there were no markings on the bloody thing!

Oh well, lesson learnt I suppose?
 
Just a quick update guys,

I’ve just heard back from my client who has informed me that according to her new plumber the thermostat was set too high resulting in nuisance tripping.

I had followed the instructions and set the stat to roughly 65 degrees, I say roughly as there were no markings on the bloody thing!

Oh well, lesson learnt I suppose?

Are you sure you read the instructions correctly? Domestic hot water is normally set to 55 degrees.

I haven't been near a megaflo for a while now, but they used to have a 1 - 5 scale on them with 4 being the 'normal' setting if I remember correctly.
 
Just a quick update guys,

I’ve just heard back from my client who has informed me that according to her new plumber the thermostat was set too high resulting in nuisance tripping.

I had followed the instructions and set the stat to roughly 65 degrees, I say roughly as there were no markings on the bloody thing!

Oh well, lesson learnt I suppose?
Earlier posts said that there wasn't a stat!
 

Reply to Scratching my head over immersion heater! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
900
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

From the front cover of the manual: Newlec Helpline: 0800 783 6909 https://www.manualslib.com/manual/3408290/Newlec-Nlsh050.html#manual I think...
Replies
1
Views
230
Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top