Hi all, daft thing to be doing at this time on a Saturday night I know but is there a reg that specifically says we must bring the installation or part of it up to the current standards if we alter it?

Also is there specifically a regulation stating that earth bonding must be upgraded or installed when changing a consumer unit
or is this just implied/best practice?
 
The regulations are not retrospective and installations do not have to be brought up to current standards. This is in the introduction.

132.16 requires that the installation be adequate and safe for any alteration or addition including earthing and bonding. This does not mean they need to be brought up to the current standard.

The regulations in general apply to all new work, but not all parts of existing installations.
 
The regulations are not retrospective and installations do not have to be brought up to current standards. This is in the introduction.

132.16 requires that the installation be adequate and safe for any alteration or addition including earthing and bonding. This does not mean they need to be brought up to the current standard.

The regulations in general apply to all new work, but not all parts of existing installations.
This is exactly the reg I’m after :rolleyes: I think I haven’t been clear as to what I meant by bringing the installation up to current standards... what I was meaning was for example sticking in an RCBO in place of an MCB when you add in extra sockets etc
 
This is exactly the reg I’m after :rolleyes: I think I haven’t been clear as to what I meant by bringing the installation up to current standards... what I was meaning was for example sticking in an RCBO in place of an MCB when you add in extra sockets etc

Ok, so in that specific example we can start with 132.16, verifying the earthing and bonding are adequate before we start work. All equipment to be used, CU and associated existing wiring and containment if any, are suitable for continued use.

RCD additional protection should be provided for sockets that you add, but not all existing sockets on that circuit need comply. Sometimes RCD protection at the circuit origin can be easiest though. All new work would need to comply with all general rules in BS7671
 
RCD additional protection should be provided for sockets that you add, but not all existing sockets on that circuit need comply.
As in most cases would the cable feeding the new sockets and the method of protection ie RCD spur etc so most of the time sticking in an RCBO would be the best way forward
All new work would need to comply with all general rules in BS7671
And so when replacing a consumer unit having altered the characteristics of each circuit care must be taken to ensure that there are no latent faults or dangerous situations which may be present in the installation.
 

Reply to Searching for regs in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thanks all. Sounds like I hadn’t completely missed the point on what Part P needs at least. I’m not so much worried about a knock on the door as...
Replies
4
Views
609
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top