Hello am i right in thinking its ok to spur off a plug socket to FCU with 2.5 twin and earth the 1.5mm flex to the Security alarm panel ? am i right in thinking reason i want to do this is because there is no space in the CU
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Security Alarm Install in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net
Very vocal these days Camerabloke.Yep that’s fine mate
ok is that allowed ?
back in box he will have to go.Very vocal these days Camerabloke
I posted that in post 4 Tel but came to the conclusion that he had the 1.5 flex already by post 7.no need for 1.5mm flex from FCU. 0.75mm on a 3A fuse is adequate.