Hi all, been reading around this and i have to admit ive quickly gone out of my depth as regards EV chargers. The charger in question is a Myenergi zappi which has its own internal RCD and PEN protection. So, the usual method it seems, is to fit another small consumer board and install a DP 32/40A (either a RCD/MCB/RCBO) with an SPD. Because of the zappi's internal rcd, it seems that an MCB is the preferred choice of protection for the cable to the charger due to selectivity. What does this mean exactly? and if an MCB is fitted, doesnt that mean the cable is only protected for overload and not for any earth faults? As always, thanks for the input.
 
Actually this is not the case. See this excerpt from the MyEnergi website:

"It is important to note that the standards for EV charge point installation usually require an RCD which meets a specific standard – IEC 61008 for an RCD or IEC 61009 for an RCBO. The RCD in zappi does not fully meet these requirements which means that a separate RCD or RCBO to these specific standards needs to be installed."
I stand corrected.
This has changed in the last year or so - previously Myenergi stated their RCDs were compliant. I double-checked with them on more than one occasion. (I also checked with NICEIC if a "Type-A + 6mA DC" met the requirements - and they said YES!) :(
 
I stand corrected.
This has changed in the last year or so - previously Myenergi stated their RCDs were compliant. I double-checked with them on more than one occasion. (I also checked with NICEIC if a "Type-A + 6mA DC" met the requirements - and they said YES!) :(
Lot's of us have been similarly burned. Napit said the same.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Suffolk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician
Business Name
Marine electronics

Thread Information

Title
Selectivity : What does it mean specifically, especially in relation to EV chargers
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
18
Unsolved
--

Advert

Thread statistics

Created
clanky,
Last reply from
timhoward,
Replies
18
Views
4,152

Advert

TrueNAS JBOD Storage Server

Back
Top