I see from the building regs, that these type of fittings need to be hard wired, and should not be installed via klick's, or any other plugin system.

Can anybody elaboarte on that?
 
Indeed

What concerns me as the testing inspector, is whether or not I should be pulling it up? The ceiling type is a metal grid system where you need a 'tool' to remove the tiles where the klicks are sited.
 
Could I point out that the use of Click roses or Gregs (if you of my generation) is perfectly acceptable for emergency fittings and exit signs (running man) so long as they are not accessible without the use of steps, which are classed as TOOLS..

If the plug in Roses are above a false ceiling then this is perfectly acceptable because under normal circumstance a person could not unplug such a fitting.
 
Yes for so called 'normal' emergency fittings, and not self contained emergency escape route lighting, which are normalyy sited above exit doors, and change of direction on the escape route.

my apologies if I was not clear before.
 

Reply to Self Contained Running Man Fittings in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
918
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi All, In need of some advice on what is and isn't allowed under regs. I'm extending a circuit in my house so I can install a socket on the...
Replies
0
Views
232
I know it was a few years ago when LED was mor in its infancy but we looked at a job that had designer flo light fittings in a big bar. The...
Replies
3
Views
420

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top