Hi all,

Newly qualified electrician here who is in the process of re-wiring my own property.

I have recently converted my old CU (if I can call it that!) in my 1950's property to a full RCBO C.U. (No SPD).
Main fuse is 100A. Double pole isolator fitted prior to C.U.. 100A double pole switch internal to C.U., 63A RCCB and then the various RCBO's to supply the house. 4 spare ways in the CU.

I have ran two times SWA supplies (10mm2) - Yes, I know overkill. This cable wasn't my first choice but was leftovers from an install job through work.

My idea is to have two dedicated supplies, one for a dedicated EV charger (7kW maximum on single phase) and then one supply dedicated for the garage. The SWA is buried direct in the ground, with some mechanical protection around the cable. I will not go near the current carrying capacity of the SWA I know but it is in there now and is done.

My questions are these however:

1. Do I run both cables to the garage and terminate both in the garage on separate secondary consumer units? EV charger CU and Garage CU?

If I was to complete this, do I just add two 50A RCBO’s (Schneider Easy9 Type B) in the house board, local rotary isolators for each CU, 40A main switch in the EV charger CU and garage CU, and then for the EV charger CU, a 32A Double Pole Type B RCD and for the garage CU, 32A MCB for sockets and 6A MCB for lights, with a couple spare ways.


2. Do I bin the separate consumer units off and just connect in the main board?

I quite like the idea of having a garage CU and EV cu closer to where I would be working/ plugging a car in.
How would I connect and protect these adequately if I was to connect ONLY in the main house? Bearing in mind 4 spare ways left in the house CU.


3. Is there an easy way of doing all of this?!

Apologies for the long windedness of all of this but would just like to clarify this all up.
Thanks in advance.
 
Last edited:
Hi all,

Newly qualified electrician here who is in the process of re-wiring my own property.

I have recently converted my old CU (if I can call it that!) in my 1950's property to a full RCBO C.U. (No SPD).
Main fuse is 100A. Double pole isolator fitted prior to C.U.. 100A double pole switch internal to C.U., 63A RCCB and then the various RCBO's to supply the house. 4 spare ways in the CU.
What is the purpose of the RCCB
I have ran two times SWA supplies (10mm2) - Yes, I know overkill. This cable wasn't my first choice but was leftovers from an install job through work.

My idea is to have two dedicated supplies, one for a dedicated EV charger (7kW maximum on single phase) and then one supply dedicated for the garage. The SWA is buried direct in the ground, with some mechanical protection around the cable. I will not go near the current carrying capacity of the SWA I know but it is in there now and is done.

My questions are these however:

1. Do I run both cables to the garage and terminate both in the garage on separate secondary consumer units? EV charger CU and Garage CU?

If I was to complete this, do I just add two 50A RCBO’s (Schneider Easy9 Type B) in the house board, local rotary isolators for each CU, 40A main switch in the EV charger CU and garage CU, and then for the EV charger CU, a 32A Double Pole Type B RCD and for the garage CU, 32A MCB for sockets and 6A MCB for lights, with a couple spare ways.


2. Do I bin the separate consumer units off and just connect in the main board?

I quite like the idea of having a garage CU and EV cu closer to where I would be working/ plugging a car in.
How would I connect and protect these adequately if I was to connect ONLY in the main house? Bearing in mind 4 spare ways left in the house CU.


3. Is there an easy way of doing all of this?!

Apologies for the long windedness of all of this but would just like to clarify this all up.
Thanks in advance.
No point having an EV CU just go direct to the EV chargepoint and don't forget to install a data cable for the EV chargepoint while you are doing it. If you are worried about local isolation for the EV chargepoint just install an isolator in the garage
A CU for the garage circuits makes sense
 
What is the 63A RCCB doing?

Why RCBO's for these 2 circuits?

If the supply is protected by a 50A OCPD then a 40A main switch is nor adequate in the garage CU!

Theres no need for a rotary isolator before the garage CU, may be sensible for the charge point though.
 
As others have said, if you are using RCBOs you dont normally also want an RCCB - as that would be cascading RCDs. Also, if the cable is armoured all the way, you dont need an RCD on the Distribution circuit(s), just an MCB - in which case, I would be inclined to run just one 10mm SWA (@ 50A) to a new CCU in the garage, where the appropriate RCD-protection can be applied. Note, some EV Charge Points (e.g. the Zappi) don't want RCD-protection at all, as it would cascade with its internal RCDs - so your secondary CCU could accomodate RCBOs and/or MCBs as required).
If the garage is any distance from the house, dont forget to consider a separate (TT) Main Earth electrode.

You could use the second 10mm SWA just for the charge point - and it need only feed an isolator switch and the charge point - but it would need carefully labelling, to avoid confusion with the local consumer unit!
 
As others have said, if you are using RCBOs you dont normally also want an RCCB - as that would be cascading RCDs. Also, if the cable is armoured all the way, you dont need an RCD on the Distribution circuit(s), just an MCB - in which case, I would be inclined to run just one 10mm SWA (@ 50A) to a new CCU in the garage, where the appropriate RCD-protection can be applied. Note, some EV Charge Points (e.g. the Zappi) don't want RCD-protection at all, as it would cascade with its internal RCDs - so your secondary CCU could accomodate RCBOs and/or MCBs as required).
If the garage is any distance from the house, dont forget to consider a separate (TT) Main Earth electrode.

You could use the second 10mm SWA just for the charge point - and it need only feed an isolator switch and the charge point - but it would need carefully labelling, to avoid confusion with the local consumer unit!
P.S. Dont forget, EV Charge Points require at least Type A RCDs upstream of them.
 
As others have said, if you are using RCBOs you dont normally also want an RCCB - as that would be cascading RCDs. Also, if the cable is armoured all the way, you dont need an RCD on the Distribution circuit(s), just an MCB - in which case, I would be inclined to run just one 10mm SWA (@ 50A) to a new CCU in the garage, where the appropriate RCD-protection can be applied. Note, some EV Charge Points (e.g. the Zappi) don't want RCD-protection at all, as it would cascade with its internal RCDs - so your secondary CCU could accomodate RCBOs and/or MCBs as required).
If the garage is any distance from the house, dont forget to consider a separate (TT) Main Earth electrode.

You could use the second 10mm SWA just for the charge point - and it need only feed an isolator switch and the charge point - but it would need carefully labelling, to avoid confusion with the local consumer unit!
In fairness I always install RCD protection upstream of a Zappi installation as the internal RCD is not to any of the following Standards: BS EN 61008-1, BS EN 61009-1, BS EN 60947-2 or BS EN 62423.
 
Also, if the cable is armoured all the way, you dont need an RCD on the Distribution circuit(s), just an MCB -

This is not necessarily true, we don't have enough information to know whether RCD protection is required or not.
If the garage is any distance from the house, dont forget to consider a separate (TT) Main Earth electrode.

Why would distance matter for this? The decision to establish a seperate earthing system would be based on bonding and equipotential zone requirements, not anything to do with distance. We know the SWA is 10mm, this is more than likely going to be 3 core so it will satisfy the requirements for bonding.
 

Reply to Separate connections to a EV charger and garage supply in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
980
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thank you everyone for your comments Celia
Replies
6
Views
702
I seem to recall that written information for their approved installers listed an explicit requirement that it be wired and connected in all...
2
Replies
16
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top