Hello,
I'm doing a periodic inspection and am unsure weather to fault this,
I have a generator which is the source of my supply, this then feeds two main distribution panels out of the main switch. So there is two 3 phase supply cables out of one MCCB. Does 314.4 come into play or does it just relate to final circuits as it states in the regs.
314.4 Where an installation comprises more than one final circuit, each final circuit shall be connected to a
separate way in a distribution board. The wiring of each final circuit shall be electrically separate from that of every
other final circuit, so as to prevent the indirect energizing of a final circuit intended to be isolated.
Or is there another regulation that i need to be looking at ? Having abit of a debate........
Cheers
I'm doing a periodic inspection and am unsure weather to fault this,
I have a generator which is the source of my supply, this then feeds two main distribution panels out of the main switch. So there is two 3 phase supply cables out of one MCCB. Does 314.4 come into play or does it just relate to final circuits as it states in the regs.
314.4 Where an installation comprises more than one final circuit, each final circuit shall be connected to a
separate way in a distribution board. The wiring of each final circuit shall be electrically separate from that of every
other final circuit, so as to prevent the indirect energizing of a final circuit intended to be isolated.
Or is there another regulation that i need to be looking at ? Having abit of a debate........
Cheers