Would like your feedback please lads. large house finished,granny flat 5 meters away.Is it ok to split feed at meter(tails junction box)and run a 10 or 16mm supply straight to flat to new cu(also taking pme earth).Not sure of all regs (must be thick the regs are not in plain enough english for me)would appreciate your help ta.
 
Just run a distribution circuit from existing CU to a new board in the granny flat. Then rig this like a new 'un, RCDs and all. Depends on access/max load etc of course, but thats the way I would do it.
Not sure waht you mean by taking PME Earth with you? A new dist would be run down a single cable from the existing board.. 5 metres is nowt
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

stidge

Arms
-
Joined
Location
Nottingham
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Clemlec

Thread Information

Title
seperate feed same supply
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
4
Unsolved
--

Advert

Thread statistics

Created
stidge,
Last reply from
stidge,
Replies
4
Views
1,742

Advert

Back
Top