Seperation

Contractor upgrading electrical installation, two compartment metal trunking, T&E in top portion and data, phone and door entry in bottom. The contractor also wants to put fire alarm cable in the trunking I said the 528-1 day should be separated they said no it’s fine. Who is right what reg could confirm contractor stance.
 
k) To avoid the risk of mechanical damage to fire alarm cables, they should not
be installed within the same conduit as the cables of other services. Where
fire alarm cables share common trunking, a compartment of the trunking,
separated from other compartments by a strong, rigid and continuous
partition, should be reserved solely for fire alarm cables.


and

l) To avoid electromagnetic interference with fire alarm signals, any
recommendations by the manufacturer of the fire alarm equipment in
respect of separation of fire alarm cables from the cables of other services
should be followed.

and

n) Fire alarm cables carrying power in excess of ELV should be segregated from
ELV fire alarm circuits by use of cables conforming to 26.2b) and with 26.2l). In
particular, the mains supply cable to any control, indicating or power supply
equipment should not enter the equipment through the same cable entry as
cables carrying ELV. Within the equipment, low voltage (LV) and ELV cables
should be kept separate to the extent practicable.


above plagurised from IET forum
 
Last edited:
k) To avoid the risk of mechanical damage to fire alarm cables, they should not
be installed within the same conduit as the cables of other services. Where
fire alarm cables share common trunking, a compartment of the trunking,
separated from other compartments by a strong, rigid and continuous
partition, should be reserved solely for fire alarm cables.


and

l) To avoid electromagnetic interference with fire alarm signals, any
recommendations by the manufacturer of the fire alarm equipment in
respect of separation of fire alarm cables from the cables of other services
should be followed.

and

n) Fire alarm cables carrying power in excess of ELV should be segregated from
ELV fire alarm circuits by use of cables conforming to 26.2b) and with 26.2l). In
particular, the mains supply cable to any control, indicating or power supply
equipment should not enter the equipment through the same cable entry as
cables carrying ELV. Within the equipment, low voltage (LV) and ELV cables
should be kept separate to the extent practicable.


above plagurised from IET forum
And tel is our resident expert in plagiarising....

car stereos, tv’s, bottles of whisky.....?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
Overcurrent,
Last reply from
i=p/u,
Replies
5
Views
1,210

Advert

Back
Top