In the original post he states a 100 A supply as I've always understood for this size incomer 25mm tails should be used (approx 114 amps) for 100A main fuse ,16mm has a rating of around 87 amps clipped direct .
ie in the op 100A main fuse to henley block separate tails to 63A 30mA Rcd
Did you read or do you know regulation 434.2.1 this regulation leads you nicely onto 434.2.2 which is the one relevant to this scenario. which I posted on my OP ? Providing the OP can adhere to the points within these regulations, which if fitting a small sub board by henly blocks the chances are he will, then he can reduce the CSA size of the tails from the henly block to the sub board.
In fact sections 433 and 434 are pretty good reads in general when providing overload and fault protection. Both these sections will give guidance as why he can fit smaller tails from the Henley block to the sub board.